Discuss What are the dangers of poor insulation resistance results between neutral and earth? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
What are the dangers of poor insulation resistance results (i.e <1Mohm) between neutral and earth?

If all other tests are ok, what are the dangers of the above?

My thoughts are it may indicate a breakdown of the insulation somewhere. However, what are the dangers of this breakdown between neutral and earth? They are both at the same potential already.

What are the other dangers? Is there a risk of fire somehow with poor N-E readings? I can't see how (if all other tests are ok). Although, perhaps the poor IR results are due to a poor connection which is heating up the cable, causing the insulation to breakdown.... so perhaps fire is a possibility?
 
What are the dangers of poor insulation resistance results (i.e <1Mohm) between neutral and earth?

If all other tests are ok, what are the dangers of the above?

My thoughts are it may indicate a breakdown of the insulation somewhere. However, what are the dangers of this breakdown between neutral and earth? They are both at the same potential already.

What are the other dangers? Is there a risk of fire somehow with poor N-E readings? I can't see how (if all other tests are ok). Although, perhaps the poor IR results are due to a poor connection which is heating up the cable, causing the insulation to breakdown.... so perhaps fire is a possibility?
Had a situation where neutral had failed at meter position so current was tracking back thro cpc because of low ir between n and e.Could have caused a fire.
S
 
As above. The danger is a failed neutral, then the cpc starts carrying the current, and, if the cpc is open somewhere, parts of the circuit and connected equipment that should be at earth potential may be raised to a dangerous voltage.
The other 'danger' is now that most circuits are RCD protected, a N-E leak will cause nuisance tripping.
 
Had a situation where neutral had failed at meter position so current was tracking back thro cpc because of low ir between n and e.Could have caused a fire.
S
I can see (with your example), how that could potentially cause an electric shock, but not a fire?
 
As above. The danger is a failed neutral, then the cpc starts carrying the current, and, if the cpc is open somewhere, parts of the circuit and connected equipment that should be at earth potential may be raised to a dangerous voltage.
The other 'danger' is now that most circuits are RCD protected, a N-E leak will cause nuisance tripping.
So apart from nuisance tripping, you would have to have 3 things for 'danger to be present'?

1. Poor IR results
2. Broken neutral.
3. Open CPC.
 
I attended a call-out a number of years ago where the neutral meter tail was broken somewhere and the entire return current for the installation was going back through a neutral/Earth fault on a lighting circuit. The cable sheath was literally bubbling from the heat generated. It's a very real fire risk.
 
1 meg is going to have little or no effect.
1 Meg is actually allowable. The problem is that it is highly unusual to get a reading like that in the fixed wiring of a standard installation. It's highly likely that there is something connected in circuit that's dragging down the reading. And until you find out what it is, it can be vexing
 
The risks arising directly from low (E.g. 0.1-1MΩ) insulation N-E are low to nil. The importance of such a reading, as hinted at above but not explicitly stated, is that it indicates that the wiring is damaged in some way and other hazards might exist that need to be investigated, more serious than the low IR itself. For example, a rodent might have stripped both the line and neutral to bare copper but at the present time only the neutral is in contact with masonry. In which case the low reading alerts and leads you to an unspecified problem, which when investigated, turns out to be high risk.

As mentioned above, hard N-E shorts are different and can cause other more serious problems quite apart from inevitable RCD tripping. With the general use of single-pole OCPD, neutral conductors are not generally protected against overcurrent other than as part of their circuit paired with a line conductor of identical rating. As soon as a main neutral connection or device (e.g. main switch N pole) other than a PEN goes open-circuit, small neutral conductors anywhere in the installation can be seriously overloaded if faulted to earth.
 

Reply to What are the dangers of poor insulation resistance results between neutral and earth? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
587
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral...
Replies
4
Views
1K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock