Discuss Farm Barn requires 3 phase + N + E! in the UK Electrical Forum area at ElectriciansForums.net

F

fochlegend

Hi,

The barn in question currently has a 230V Supply, 3 core 16mm SWA is used for this. There is one ring main (32A) and three lighting circuits (3 x 6A) installed in the barn.

The farmer has fitted a new pressure washer in this barn that requires a 3PN+E supply (16A).

The supply to this barn comes from a 3 phase, N + E mains board about 50 metres away, I was hoping to change the three cores to a 3 phase 415v supply.

My query is...can i use an earth spike to earth the barns mains board or is the armour of the cable enough? And then to reinstate 230V to the barn should I fit a 415 to 230v Transformer? How do i work out what size of transformer I will need to do this?

Thnaks in advance

(a farm hating sparky)
 
That's a fudge if ever I heard one. Might not be a whole lot cheaper than running a new submain with a neutral either. Earthing in agricultural premises may need special consideration to minimise voltage gradient, difficult to advise without site survey.
 
Hi,

The barn in question currently has a 230V Supply, 3 core 16mm SWA is used for this. There is one ring main (32A) and three lighting circuits (3 x 6A) installed in the barn.

The farmer has fitted a new pressure washer in this barn that requires a 3PN+E supply (16A).

The supply to this barn comes from a 3 phase, N + E mains board about 50 metres away, I was hoping to change the three cores to a 3 phase 415v supply. Where are you going to get a N from?

My query is...can i use an earth spike to earth the barns mains board or is the armour of the cable enough?depends on present earthing system And then to reinstate 230V to the barn should I fit a 415 to 230v Transformer?No,You will end up with a 230v 2 phase system,not a phase and neutral. How do i work out what size of transformer I will need to do this?

Thnaks in advance

(a farm hating sparky)

Replace the distribution circuit.
 
Seems he wants to use all 3 cores of the existing cable as phases, leaving him without the neutral he now has, so only 400V. Then to supply 230V locally by stepping the 400V down. Sort of roundabout bodge I'd do to get something going in an emergency.
 
So you have a 3 core 16mm SWA and you need 3P+N+Earth in the barn for the pressure washer, and if I'm reading your thread correctly you want to use the existing 3 core as a 3 phase supply, where are you getting the Neutral from?
 
Deriving it from the TP supply with a DY tx...
 
A single phase to 3 phase convert or would be cheapest.

We had them at the wholesale nursery where I had my first Saturday job, they ran the irrigation pump, potting machine and bulk elevator. The site only had a single phase supply
 
That's the most sensible option but the economics will be dependent on the pressure washer starting and running loads, and whether the VD is just too great with the entire load on one pair of conductors. Specs needed...
 
Hi,

The barn in question currently has a 230V Supply, 3 core 16mm SWA is used for this. There is one ring main (32A) and three lighting circuits (3 x 6A) installed in the barn.

The farmer has fitted a new pressure washer in this barn that requires a 3PN+E supply (16A).

The supply to this barn comes from a 3 phase, N + E mains board about 50 metres away, I was hoping to change the three cores to a 3 phase 415v supply.

My query is...can i use an earth spike to earth the barns mains board or is the armour of the cable enough? And then to reinstate 230V to the barn should I fit a 415 to 230v Transformer? How do i work out what size of transformer I will need to do this?

Thnaks in advance

(a farm hating sparky)

Hi, would recommended that a new supply is installed to the barn, remember that a farm supply must be TT and with all correct RCD fitted. The cheapest thing to do is cant the farmer relocate the power washer or exchange for a single phase one??

Thanks
 
Hi, would recommended that a new supply is installed to the barn, remember that a farm supply must be TT and with all correct RCD fitted. The cheapest thing to do is cant the farmer relocate the power washer or exchange for a single phase one??

Thanks

Where in the world did you pick-up that that load of rubbish from??
 
Hi, would recommended that a new supply is installed to the barn, remember that a farm supply must be TT and with all correct RCD fitted. The cheapest thing to do is cant the farmer relocate the power washer or exchange for a single phase one??

Thanks
Regulation number please.
 
...The rod-god has a point...i have been in the agricultural job most of my life,and i can definitely assure you they are not all TT,and some,have the barest minimum of residual contrivance doodahs...this may just be such a scenario...:conehead:
 

Reply to Farm Barn requires 3 phase + N + E! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
682
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
616
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I’m installing 20KW of Solar on my Barn roof, The barn is fed from a 3 phase supply originating at the house which is 80 meters away. I’ll be...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock