Can't you install a second RCCD and split the loads with standing leakage between the two. This should bring it back to within the 30mA threshold.

It's a split board already, and shoe-horned into a tight space so fitting another CU won't work.

@Spin - reason for still wanting to have them on RCD is simply that the heaters themselves are vulnerable to things like drinks spills, toddlers pulling on the inlet cables etc. So yes, whilst I could probably justify having them only on MCB's, I'd rather have them with some leakage protection, even if it's higher than usual. And yes, I did of course mean departure!

All of this, and reading Ackbar's thoughts, begs the question of what do we do as installers and designers to slow this process down in the future. Are we really going to start installing high integrity circuits in domestic houses, splitting circuits down to 1-1 configurations on RCBO's etc? So much technology in peoples houses now, no chance of that slowing down, so what do we to future proof? I've just done a tender / design on a massive 'grand designs' kind of build, and it's almost pretty much one rccb, one cable, one outlet. Big expense.
 
I never thought of RCBO's, we don't see them much where I am. I would say these are the way of the future, a single RCCD is putting all your eggs in one basket when it comes to an earth leakage fault (or overall accumulation in your case). It's the equivalent of running multiple socket circuits on a 60A MCB and expecting it to effectively protect them. If RCBO's are economically viable and they fit into a single space in the CU then they have to be the best option.
 
Hi,

Split board with two RCD's that ramp test to around 21-22mA each
to minimise the nuisance tripping is to put the two heater circuits (being the most individually leaky) onto individual 100mA RCBO's and declare them as dedicated circuits

It's a split board already, and shoe-horned into a tight space so fitting another CU won't work.

I may be missing something here, but if it is a split load board already, protected by two 30mA RCD's, one for each side, then how is it possible to fit 100mA RCBO's ?, as this will not solve your problem, as the 30mA RCD's will still trip before the 100mA RCBO's, as there is no discrimination whatsoever here, the only way would be to put a mini CU fed with tails from the incoming side, as others have already suggested.

What Iam saying here, is you will have 30mA RCD's feeding 100mA RCBO's.
 
Last edited:
I may be missing something here, but if it is a split load board already, protected by two 30mA RCD's, one for each side, then how is it possible to fit 100mA RCBO's ?, as this will not solve your problem, as the 30mA RCD's will still trip before the 100mA RCBO's, as there is no discrimination whatsoever here, the only way would be to put a mini CU fed with tails from the incoming side, as others have already suggested.

What Iam saying here, is you will have 30mA RCD's feeding 100mA RCBO's.

You are!! The board gets reconfigured as a three-way, so 2 x 30mA RCD's feeding whatever, and then two separate RCBO's on the same DIN rail but fed directly. Simples.
 
Last edited:
Then surely if your just going to have 2 X heaters on an RCBO on an high integrity side 30mA RCBO's will be enough? surely the 2 heater alone can not produce 20+ mA Protective conductor current and i'm sure you said in a previous post that they only produced about 5mA a piece, this way you would not have to worry about not having additional protection problems
 
68, I assume he's going to fit the 100mA RCBOs into the high integrity section of his CU, ie the bit fed straight off the main isolator :)

You are!! The board gets reconfigured as a three-way, so 2 x 30mA RCD's feeding whatever, and then two separate RCBO's on the same DIN rail but fed directly. Simples

Ahh!,
I had a look through the previous posts, and did not see anywhere it mentioned three way boards, and thought at first you were going to add a mini CU, but if you are going the Three way with RCBO route, then I would do as others have said, and put the heaters on their own 30mA RCBO's, or two per RCBO, then it will still comply with buried cables etc..etc., and the leakage will still be within bounds.

I think you may be correct though, the way things are going RE: amount of home IT and electronic gadgetry in houses now, we maybe going the RCBO route more often than in the past.


Thanks for clearing that up.


All the best Spark 68

Cross posted with Malcom
 
Last edited:
Rockingit, if there is no requirement for 30MA RCD protection on these circuits, then providing 100mA RCD protection will not be a departure.
However if there is a requirement for 30mA RCD protection, perhaps due to cables being concealed in walls, providing 100mA RCD protection would be a departure, onlly not an acceptable one, because it would not offer the same degree of safety as would be achieved with providing 30mA RCD protection.
 

Reply to Fault driving me mad!! in the Australia area at ElectriciansForums.net

Similar Threads

A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
863
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
838
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
165

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock