Discuss Fault Find - advice please! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
15
Team - I'm after some help on a fault find that I was at this week and to work out if there's something obvious that I've forgotten, overlooked. I've only been working as a spark for a couple of years, done my city & guilds 2365 - L2&3 and done my AM2, just wanting to finish my portfolio for my NVQ - (just ome back ground to get me out of the DIY forum).

Customer reports RCD trip on down stairs ring circuit, MK split load board, half RCD protected, and half isn't. After a lot of messing about working out what was and wasn't on the circuit, eventually removed all the loads (found a few hiding) and IR tests commence. RCD is a MK 80a - 3oma, fault appears to be intermittent but there is no issues when the down stairs ring is switched off - so I'm happy that is where the problem lies.

L-E 530 MΩ, N-E 383 MΩ, L-N >999 MΩ- I measured this at the board and at a socket on the down stairs ring.

There is a brake in the ring on the line conductor, which I think is a historic problem, contained within one of the spider web of junction boxes underneath floorboards upstairs, which are underneath a very expensive floor. I have explained the need to trace it. – however the customer has sold the house to a developer who is only a couple of months away from levelling the place.

RCD test - trips @ 1/2 rate when testing on that circuit. So I disconnected the down stair ring and ramp test it from upstairs - trips @ 19ma. I thought it was a bit sensitive, so swapped it out for a new one. Same story, however the RCD holds now and does so for some time. 4 days in one instance.

But when the loads start to be plugged back in – The only thing I had in was the fridge freezer and the TV (which is in three way adapter thing) virgin media box. I’ve checked the fridge freezer cpc with a clamp meter on an extension lead – no issues, trips whilst I’m there. I take the freezer out and fridge and trips 5 mins later. The only thing in is the tv / media thing. Checked that with a clamp meter and no issues. I’ve left the client after a good few hours and I started to struggle to see the wood for the trees by this point. So I told him to take that out and slowly put things back in at 30 minute intervals – thinking could it be an intermittent fault with an appliance like a compressor on a fridge that isn’t constantly running?

So my questions are this – why would the rcd trip at half trip current on that circuit only, with no loads, despite good IR tests - is it still likely to be fixed wiring?

Could the TV / media thing have a component that is intermittently working and faulty? – When I suggested the tv he did say his son had had the back off and fitted his own speakers to it……. (my ears did ----- up at that)

Testing with a new megger mft 1711 by the way.

Anything I’ve forgotten – if it’s obvious – please don’t shoot me, it’s been a long day!
 
Last edited:
YOU COULD STARTBY TYPING IN A FONT AND SIZE THAT I CAN READ WITHOUT A MAGNIFYING GLASS.:D:D.
soz aboutthe caps.was rthe lock after givingmyreg.to the tollbridge so they could rob me a gain.
 
Team - I'm after some help on a fault find that I was at this week and to work out if there's something obvious that I've forgotten, overlooked. I've only been working as a spark for a couple of years, done my city & guilds 2365 - L2&3 and done my AM2, just wanting to finish my portfolio for my NVQ - (just ome back ground to get me out of the DIY forum).

Customer reports RCD trip on down stairs ring circuit, MK split load board, half RCD protected, and half isn't. After a lot of messing about working out what was and wasn't on the circuit, eventually removed all the loads (found a few hiding) and IR tests commence. RCD is a MK 80a - 3oma, fault appears to be intermittent but there is no issues when the down stairs ring is switched off - so I'm happy that is where the problem lies.

L-E 530 MΩ, N-E 383 MΩ, L-N >999 MΩ- I measured this at the board and at a socket on the down stairs ring.

There is a brake in the ring on the line conductor, which I think is a historic problem, contained within one of the spider web of junction boxes underneath floorboards upstairs, which are underneath a very expensive floor. I have explained the need to trace it. – however the customer has sold the house to a developer who is only a couple of months away from levelling the place.

RCD test - trips @ 1/2 rate when testing on that circuit. So I disconnected the down stair ring and ramp test it from upstairs - trips @ 19ma. I thought it was a bit sensitive, so swapped it out for a new one. Same story, however the RCD holds now and does so for some time. 4 days in one instance.

But when the loads start to be plugged back in – The only thing I had in was the fridge freezer and the TV (which is in three way adapter thing) virgin media box. I’ve checked the fridge freezer cpc with a clamp meter on an extension lead – no issues, trips whilst I’m there. I take the freezer out and fridge and trips 5 mins later. The only thing in is the tv / media thing. Checked that with a clamp meter and no issues. I’ve left the client after a good few hours and I started to struggle to see the wood for the trees by this point. So I told him to take that out and slowly put things back in at 30 minute intervals – thinking could it be an intermittent fault with an appliance like a compressor on a fridge that isn’t constantly running?

So my questions are this – why would the rcd trip at half trip current on that circuit only, with no loads, despite good IR tests - is it still likely to be fixed wiring?

Could the TV / media thing have a component that is intermittently working and faulty? – When I suggested the tv he did say his son had had the back off and fitted his own speakers to it……. (my ears did ***** up at that)

Testing with a new megger mft 1711 by the way.

Anything I’ve forgotten – if it’s obvious – please don’t shoot me, it’s been a long day!
Where did you ramp test the RCD?
 
I think the previous RCD was waiting to be replaced like you've done.
If the only thing connected is the T.V and it trips then it sounds like the likely culprit.
Is there is a break that cannot be found then do we split into two radials, tin hat on
 
Remember your ir tester does dc but the mains is ac, you could have a capacitive leak.
Try putting a meter on the (Edit): live conductors of the circuit to see what the normal leakage is and then connect the loads. Could just be an accumulation of leaky devices.
Edit sorry brain fart on which conductors the rcd measures:rolleyes:
 
Last edited:
I think the previous RCD was waiting to be replaced like you've done.
If the only thing connected is the T.V and it trips then it sounds like the likely culprit.
Is there is a break that cannot be found then do we split into two radials, tin hat on
Yep - that will be my next move, not ideal, but customer has sold the house and renting it off a developer until they complete on their new house. Thank you
 
RCD test - trips @ 1/2 rate when testing on that circuit. So I disconnected the down stair ring and ramp test it from upstairs - trips @ 19ma. I thought it was a bit sensitive, so swapped it out for a new one. Same story, however the RCD holds now and does so for some time. 4 days in one instance.

freezer cpc with a clamp meter on an extension lead – Checked that with a clamp meter and no issues.
So my questions are this – why would the rcd trip at half trip current on that circuit only, with no loads, despite good IR tests - is it still likely to be fixed wiring?

You should test the RCD at the RCD with outgoing circuits disconnected not from remote points on a circuit, especially not a circuit known to have a fault.

Are you using a standard clamp meter or one designed to measure earth leakage/very small currents? An earth leakage clamp meter should be put around all live conductors to measure earth leakage rather than measuring the earth current.

The RCD would trip at half current when tested in circuit because the earth leakage on the circuit will bias it to trip, this is why you don’t test RCDs this way.
 

Reply to Fault Find - advice please! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
806
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock