Discuss Fault finding - insulation testing in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
19
Hi everyone, did some insulation testing on my mates house as his RCD was tripping manage to isolate it to the ring circuit, Live-Earth for the ring circuit came to 0.01Mohms and all appliances have been disconnected and removed.

However I have disconnected the Live-Earth behind one socket (Socket A) in order to split the circuit and with the process of elimination work out and get closer to where the fault is.
I got readings of >900 for another socket in the same room (Socket B) but when i reconnected the Live-Earth in that Socket A and tested Socket B again just to make sure the reading fell to 0.03Mohms.

Theres no clear correlation to which sockets are ok and which aren't for instance there are four double sockets in the living room all will have a reading of 0.03Mohms but one will be >450Mohms and the dining room next door also has 4 double sockets and two have given a low reading of 0.02Mohms and the other two have >550Mohms, any ideas?

Thanks in advance.

Mark
 
It sounds like you have got joint boxes under the floor feeding various different sockets.If you cannot break the ring to find the fault then usually i would remove all the sockets and using a trailing lead test between each pair of wires to determine where they go.Draw a diagram of the rooms and overlay the schematic of where each wire goes.Only then can you make sense of how it's been wired,how many joint boxes there are and ultimately where the fault is.

It sounds like damp from your readings.Could be in a joint box under a wet floor or in the back of a socket on a damp wall.
Good luck finding it!:p
 
I can't quite make out what you are doing tbh .... Have to checked the continuity of the ring and tried to determine which are Spurs?

Sound to me as if you could have an old ring, with junction boxes under the floor and Spurs off Spurs .....

Had something very similar earlier this year .... Different ages and types of cable too
 
It sounds like you have got joint boxes under the floor feeding various different sockets.If you cannot break the ring to find the fault then usually i would remove all the sockets and using a trailing lead test between each pair of wires to determine where they go.Draw a diagram of the rooms and overlay the schematic of where each wire goes.Only then can you make sense of how it's been wired,how many joint boxes there are and ultimately where the fault is.

It sounds like damp from your readings.Could be in a joint box under a wet floor or in the back of a socket on a damp wall.
Good luck finding it!:p

I'm going back tomorrow evening to have another try this time disconnecting all Live-Earth conductors from behind the sockets and doing individual IR tests along each hopefully to find the problem. I had thought about joint boxes under the floors, my mate bought the house of a guy who had bought it to 'refurb and sell on job' and he doesn't have any testing certificates for me to go off.
Yes I've already prepared a diagram ready for tomorrow, I hope it isn't damp...... It has been chucking it down the past few days!
 
Don't start with IR tests. Do as mentioned above and use continuity tests e.g. on the N conductor, to trace the wiring. Then, the IR tests you do will be much more meaningful as you know which parts of the cabling they will reach.

An L-E of 0.01MΩ is very low even for a damp fitting, but you aren't getting much useful info from using the IR range bottomed out like that with just one digit reading, it could be one ohm or ten thousand, so you don't know what kind of problem to look for. Test the IR with your DMM or 250V or continuity range and see just what it is like. If it reads say 10Ω you know it is an intermittent short that will probably be scorched and smell of burnt stuff. If it's 15,000 ohms then it might just be damp.
 

Reply to Fault finding - insulation testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
455
Quick question. I am new to electrical installation so please be patient. You guys are great at answers. Re Insulation Testing. Why if I test...
Replies
12
Views
807
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
568
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
989

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock