Discuss Fault on PV System in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

N

norfolksparky

Hi all,

I am new to the forum so be easy! Lol!

I have installed a 2kw pv system on a house near me 8 panels, sma 2000hf inverter etc etc. I have fired the system up but have only got 0.8A and 104 watts. The sun is blazing here today and can't work out why. I will head back tomorrow to investigate and wondered if anyone can give me some advice as a heads up. I am a sparky by trade so fairly clued up on watts, amps, voltage, volt drop etc etc.

Thanks
 
Voltage on the inverter states 272v and current 0.8A. I am yet to try the Isc as I didnt have time, just turned it off until tomorrow. i measeured the Voc of the string and found 272v so figured things were looking good, until I turned it on! Lol!
 
No it was designed by supplier, Ubbink! The panels are Voc 37.2v Isc 8.42A. Can you give me some expected test results before I start please. The only thing was an eversolar inverter was specified but it turned up damaged and they dropped of the sma and said it would be fine?
 
No it was designed by supplier, Ubbink! The panels are Voc 37.2v Isc 8.42A. Can you give me some expected test results before I start please. The only thing was an eversolar inverter was specified but it turned up damaged and they dropped of the sma and said it would be fine?


What make model no and wattage our the panels
 
No it was designed by supplier, Ubbink! The panels are Voc 37.2v Isc 8.42A. Can you give me some expected test results before I start please. The only thing was an eversolar inverter was specified but it turned up damaged and they dropped of the sma and said it would be fine?

ubbink 250wp modules???????????
 
The panels are Ubbink but I can't find any info on them i think they are made by someone and re labelled/brended which doesn't help. Think i will stick to know brands from now on. What sort of readings should I be expecting?
 
Voc = 297v allowing for tempreture i would be expecting to see 280-290 - Isc is 8.42@ STC, so expect to see 2-3amp, maybe more, i dont often see Isc at STC figures, on a dull day you'd be lucky to get anything over 1 amp.

Testing VOC is a different reading to what the inverter is seeing, inverter will display running voltage rather than open ended voltage - relax man.

Added: Ubink are Delsolar panels.
 
Last edited:
so why the 0.8A running and only around 110 watts? The Irradiance was off the scale of the meter, the sun was blazing hot! Ouch red all over! LOL!
 
What time was it? was it shaded by scaffold pipes? trees? theres 2 reasons why - if the VOC is correct then you know the string is wired correct. It only takes 1,2 or 3 scaff pipes to shading 1 or 2 panels at it will drag the system down something silly.
 
there was a couple of panels shaded yesterday but tried it again today when it was in full sun and it was the same ish, wattage 66 watts. I have set the inverter to G83 already aswell.
 
I'll put a tenner on the system being significantly shaded. Hopefully only by the scaffolding as Dan says.

A tiny bit of shading run the wrong way across the bypass diodes / strings of cells on the panels can cause a hell of a drop in output.
 
If there was a small amount of shading would it pull it down that much? from would i think should be 1500w to 1700w to around 100 watts? The system only generated 4.4 kw/hr today?
 

Reply to Fault on PV System in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I am a Napit registered electrician and want to get into Solar PV and battery storage. I have boot camp booked in April but am not hearing good...
Replies
1
Views
365
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
770
Hello everyone, I currently have two solar modules left over from an installation and I would like to use them to set up a solar system on the...
Replies
3
Views
911
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
943

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock