It appears that this installation may well be classed as Agricultural/Horticultural.
As such, I would suggest a perusal of Section 705.
The circuit supplying the shed will require a minimum of 300mA RCD protection.
The socket-outlet circuit will require 30mA RCD protection.
The shed will most likely require bonding, as it's an extraneos-conductive-part.
If the earthing system is TT, then the disconnection times will be 1s for distribution circuits and 0.2s for final.
 
Why's that then?


You started by saying that you were sending a supply out from a main CU to a shed, which most people can easily relate to. Now it appears that the main CU is already in an outbuilding itself and your "shed" is a massive aluminium conductor in direct contact with earth. You haven't told us anything about your main earthing arrangements or whether there are still horses in the vicinity.
I merely meant that the situation seems more complex than the OP suggested and that most people would keep out of this thread without seeing your exact setup. No disrespect meant at all.
 
This seems to be getting a little confusing so I'll start again with the exact set up.


Firstly there is no house.
The tac room has its own supply from the main supplier which is a TNCS system
there is 1 socket in the tac room and 1 light in each of the stables so 9 lights in total, the light switch for each stable is on the outside of each stable out of reach of any horse and in an IP66 enclosure.
the lights are fed by 1.5mm singles in 20mm PVC conduit over 2m high and inside
There is a 30mA RCD in the CU protecting all circuits

The shed
I want to put 3 x double sockets in here with 2 x flourescent lights.

I will run 4mm singles in conduit to an external junction box where I will come from there in 4mm SWA to the 2 way CU in the shed
I will feed this by a 32A breaker in the main CU and use the main RCD to protect this circuit
I will of course bond the shed.

how does this look?
I appriciate the help with this
 
will it be a 3 core SWA? make sure the SWA is bonded, and i think you may have to run a 10mm earth back to the MET to bond the shed/lorry
 
To start with, use of a TN-C-S supply appears to contavene both BS7671 and ESQCR.
Is the main supplier aware that the installation is using their PME connection?
If you intend bonding the shed, as the supply is TN-C-S, a 10mm² conductor will be required, or the shed will have to made TT.
 
Thank you for clearing that up robbo. How far is the lorry/shed from the main CU? Just wondering if 4mm will be adequate as you are feeding it from a 32A supply. Have you done the VD calcs?
Also, regarding the bonding, what spinlondon said.
 
Thank you for clearing that up robbo. How far is the lorry/shed from the main CU? Just wondering if 4mm will be adequate as you are feeding it from a 32A supply. Have you done the VD calcs?
Also, regarding the bonding, what spinlondon said.

The shed is just under 30m away from the main CU I have looked at table 4D1 Ref Method B and 4mm will carry 32A the voltage drop on that was 4.47% (10.5v) which is within the 5% drop allowed.
I can always Reduce this to 20A as there will never be that kind of power going through it, all he has in there is a chop saw, table saw and a few battery chargers and these will never all be being used at the same time.

I will do that with the bonding then and take a 10mm back to the MET

Many thanks
 
Have you allowed for the fact that your conduit cables are rated differently to your armoured in your calcs, plus did you say there will be several running together in the conduit, hence temperature factors? Just thinking aloud as it is an assessment job...
 
Have you allowed for the fact that your conduit cables are rated differently to your armoured in your calcs, plus did you say there will be several running together in the conduit, hence temperature factors? Just thinking aloud as it is an assessment job...

I hadn't no, thanks for pointing that out. i will use a 20A in the main CU.

Many thanks
 
I hadn't no, thanks for pointing that out. i will use a 20A in the main CU.

Many thanks

Which I was going to use in the first place as I thought it was a bit close but someone mentioned in one of the earlier posts that I could go 32A but they wouldn't have known to take the other factors into consideration either.

I bet you have quite a vivid image of this installation now :) thank you for all of your comments.
 

Reply to Feeding a Shed Cu from the main CU in the Australia area at ElectriciansForums.net

Similar Threads

Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
935
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
527
Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
998
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
722
Gday lads. Have a question about a 3 phase shed feed. I have a roll on 16mm2, 3 core and earth orange circular. Can I run a 16mm2 SDI neutral in...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock