why are you notifying it? no one is allowed to come into my house to check my Electrical system lol, if you used to be a spark as you mentioned and know what you are doing then just get on with it. Okay back to the job, one thing I would say is whether the supply to the cabin at 4mm2 may be a little small and maybe a 6mm2 would be better, a freezer and light in the first shed is literally no load so there is some capacity for the log cabin, I would not go smaller than the original shed supply but that's me, by the way a lot of guys on here are newly out of college so my comments may shock them but lets be honest here, if it is your house then do what you want, just disconnect everything before you move hehe.Hi guys,
I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a single socket for a freezer unit. I also have an additional 32 Amp (idle).
Now I have a log cabin 10m away. I am going to install a new consumner unit in the LogCabin and feed it from the 32 Amp MCB via a 4mm SWA cable. This Log cabin CU will have the same stuff (perhaps a 16Amp RCBO for 2 Radial sockets and a 6 Amp RCBO for lighting.
Regardless of it being notifiable etc , any suggestions objections are welcome.