Discuss Ferrule crimping tool in the Electrical Tools and Products area at ElectriciansForums.net

I need a recommendation for a decent ferrule crimping tool, particularly for shortening RCBO neural and earthing wires for connection into the bars. Thanks.
Not an answer but another question. Or two? Why do you want to apply a crimp to the shortened cable? Strip it, twist it and torque to the required setting?

but I hold no electrical qualifications!
 
Not an answer but another question. Or two? Why do you want to apply a crimp to the shortened cable? Strip it, twist it and torque to the required setting?

but I hold no electrical qualifications!

Because of regulations mate.
526.9.1 In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.

1591253578135.png
 
Last edited:
Not an answer but another question. Or two? Why do you want to apply a crimp to the shortened cable? Strip it, twist it and torque to the required setting?

but I hold no electrical qualifications!
Stranded cable should not be tightened under a screw, it damages the strands. The ferrule keeps the strands together and then the screw tightens onto the ferrule which stops the strands splaying, breaking or twisting.
 

Reply to Ferrule crimping tool in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

As I have retired now (really!) I have decided to sell my electrical tools etc. They include hand tools, hilmor galv. conduit bender 20/32 with...
Replies
12
Views
1K
Hello everyone. What tool would I need if I were to work on a construction site doing containments? Thank you
Replies
5
Views
782
Hi Guys Think it's time I brought myself a 'decent' punch down tool. Any recommendations would be appreciated ? Been eyeing up both of...
Replies
8
Views
509
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K
Inspired by another thread, which I don't wish hi-jack. Can anyone recommend a decent, relatively low price punch down tool? I've had a cheap...
Replies
2
Views
573

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock