Discuss Fire alarm cabling student accommodation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
hi all!

I’m working on a new build student accommodation block wiring for fire alarm.

I have been instructed to use perforated banding as containment across the stud walls above the ceilings as they won’t allow us to put any containment up. Now this to me feels a bit dog rough.

Can anybody shed some light on this if it is even allowed?

Thanks in advance
 
Cable fixings for fire alarm cables should have the same or better fire protection as the cable. Ask to see proof of this.
 
Dropping loops of banding from a concrete ceiling to support the cable between the studs would work. Use concrete screws, not wood screws and plastic plugs, to ensure the fixings don't let go in a fire.
Theres too much over thomking now a days with fixings, if the fire is hot enough to cause the plugs to release the scree from thr concrete the fire is going to was out of control by then and the least of the worries of anyone in there will be some loose dangling cables as everything else will be in the way too that os fixed too a wall in that way.
 
I have to disagree; two firefighters and a member of the public died in the Harrow Court fire due to entanglement with electrical cables; not some other part of the building fabric. Do you really not care about your work and the impact it has on others?
 
I have to disagree; two firefighters and a member of the public died in the Harrow Court fire due to entanglement with electrical cables; not some other part of the building fabric. Do you really not care about your work and the impact it has on others?
How was it originally contained?
 
I have to disagree; two firefighters and a member of the public died in the Harrow Court fire due to entanglement with electrical cables; not some other part of the building fabric. Do you really not care about your work and the impact it has on others?

Was that specifically through the failure of plastic real plugs or was it trunking, clips, cable ties etc which failed?

It is not a case of not caring, it is a case of understanding what is or is not a risk.
 
I believe the bre have carried out tests specifically on fixings of supports in light of the Harrow Court and other incidents. They found the use of plastic wall plugs to be inappropriate in these situations and all metal fixing would be best used. Something like Dewalts wall dogs (other brands are available).
 
I believe the bre have carried out tests specifically on fixings of supports in light of the Harrow Court and other incidents. They found the use of plastic wall plugs to be inappropriate in these situations and all metal fixing would be best used. Something like Dewalts wall dogs (other brands are available).
You got a copy of the report to back this up?
 

Reply to Fire alarm cabling student accommodation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
I posted last week regarding a lighting cable being too short in the wall to reach my new light fittings.this is still annoying me lol, I will try...
Replies
8
Views
2K
I’m in the process of changing my old downlights in the bathroom , I put them in years ago with advice from my late father who was a sparky, these...
Replies
1
Views
1K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Hello i've recently just had a re wire done on a three bed semi house, Ive noticed a few things im not 100 percent on ive spoken to the firm that...
Replies
24
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock