Hi,

I would be grateful if anyone could confirm the certification required for the addition and extension of a fire alarm. Scenario is, I have installed the fixed wiring for the alteration to an addressable system as per their drawings, fire alarm contractor will commission.

I assume I can cover this with a MWIC as it technically an alteration of an existing circuit?
 
If you have altered the zone/sounder circuits you need a modification certificate as recommended in BS5839:1.
 
It depends on what has been agreed, the commissioning person may be doing his own testing as the documents are likely to require all the resistive values etc to be logged for future ref'.
I have installed many systems where we have had to get in the manufacturers own teams in to commision an install, on occasion they do all the testing and logging, on others they are happy for you to do it and will document your results.
 
Unfortunately myself and FA contractor are unlikely to cross paths as they are not due to commission until May.

My remit was to provide the fixed wiring alterations and containment to the drawings provided by the FA contractor.

I have tested the newly installed cabling and have the results, IR and continuity. 3 separate circuits in total. It just how I document this, mainly to cover myself as I will not be going back to this job come next week.

Thanks for your replies gents
 
Take your own readings just for confirmation, and record them on a sheet. Maybe forward to person ordering work if youl not see the fa guy.
 
Sometimes just writing an old fashioned letter has it's value. If you say the work is complete, the new wiring is tested, and you are assuming that the commissioning contactors are taking care of all certification required you have covered yourself and given them a chance to disagree.
 

Reply to Fixed wiring testing required for an addressable fire alarm system? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am doing renovation to a cafe in Scotland at the moment and after speaking to the local council the building requires the minimum standard for a...
Replies
5
Views
1K
Hi all, I currently have a Pyronix Enforcer V10 Wireless alarm system. I have some shock/contacts on windows, doors, PIRs, and an external siren...
Replies
0
Views
761
Hello, I applied for a retrospective completion certificate for kitchen relocation. The work was done about 7 years ago. The building standard...
Replies
26
Views
6K
Hi, My alarm system is a Texecom control unit (Premier 64-w) + Keypad + Sounder, and is using the wired zones 1-4 only, with no additional...
Replies
2
Views
2K
Good evening all, I have added an extra smoke alarm to an extension that I have just finished. I have been asked to provide a fire alarm...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock