Deleted member 105018

Hi there folks. Advice needed. Asked to look at an issue with some MR16 LED lamps. Cut a long story short there is 13 x 5w LED MR16s on a radial circuit of length approx 30m long. Lamps placed relatively equidistant along the circuit.

Constant Voltage driver being used (mean well) at 15v to cater for 3v drop over cable length. Supposedly lamps are good for 9-18vdc. Anyway on power up the lamps are flashing. Not flickering. Looks like the driver power the lamps up and then disconnects before trying again. Immediately I thought that the driver may be going into over current on power up but the driver is rated at 100w on a 65w load circuit. Tried a bigger driver (120w) and still the same. Tied the two drivers together (to give 220w) and still the same.

If I remove 6 of the lamps the rest stop flashing and then by adding each removed lamp individually they stay lit properly (which kicked off the over current theory)

Any ideas much appreciated? Thanks.
 
To be fair to the company who have sold the driver they’ve suggested this but I’m reluctant because it means rewiring the lamps in series and then you’ve got the old Xmas lights scenario when a lamp goes. But if that’s what it needs then that’s what it needs.
 
I'd try it with a known 12V supply, old style transformer or car battery if it's all you can find. It sounds like the lamps don't like the supply for some reason, are you sure they're ok with 15V and are you sure the supply is providing 15V, even with a low load?

Normally it's not necessary to dial the voltage up for LED's, the internal inverter will provide the required current to the LED even if the voltage is at the low end of the range.
 
Yeah I wondered if the electronics in the driver are “too clever” for the internal electronics of the lamps and something is causing the driver to trip. Say a capacitor or whatever. I wondered about just a bog standard 12v psu or even just a 240 - 12vac transformer. I did test the lamps on a bench top supply and in fact they are good down to 9v so like you say it doesn’t seems that the voltage is as much as an issue as I first thought. Thanks for your input guys.
 
My understanding is that MR16s will take AC as there is a built in rectifier. That said I’ve not tried it. 240v would be ideal but the spec calls for extra low voltage as it’s external.
 
The constant voltage driver probably has a built in protection circuit, this protection circuit is objecting to the start up surge of all the lamps together,try using an NTC thermistor.
 

Reply to Flashing LED MR16s problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
518
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
729
Hey folks, i work for a relatively small company, but we are doing some big jobs. And right our headache is taking over outdoor lighting...
Replies
4
Views
1K
Hi there, I'm currently working on a project where I'd like to slowly fade the brightness of a series of high brightness RGBW LEDs. Basically...
Replies
3
Views
927
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock