Flex for fixed wiring

Discuss Flex for fixed wiring in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
116
Would you suggest flex for fixed wiring on an EICR is a C3? The client has basically run flex from one socket to a surface socket (i.e. a glorified extension lead). However I would say this is fixed wiring.

What does 521.9.1 mean where it states "only where the the relevant provisions of the regulations are met"? Does this mean CCC, installation method, overload protection etc.
 
The regulations do indeed allow flex to be used as fixed wiring as long as it’s the heavy duty type unless the risk of damage during installation is low etc etc, types of flexes are given in bs en 59565-1
For more detail see regulation 521.9.1 page 126 of bs7671.
 
Interesting timing ...........over in the plumbers forum I have just said that as far as I'm concerned boiler wiring is "control" wiring and therefore use of 5 core "flex" is perfectly acceptable......

off to my bunker now with tin hat on!

Hello Murdoch,

Thanks for your Expert opinion - I am pleased that you would be happy for Flex to be used to wire Heating System Controls / `Controls Wiring`.

Although as I mentioned Electricians carried out the wiring on my Heating systems - usually because the Builder / Customer always wanted only ONE Electrical Contractor / Electrician certifying the whole property`s Electrical Installation - and therefore the wiring was `nothing to do with me` - I still was not completely happy that `My System` had been wired correctly.

I am also pleased to see Member Dave OCD`s message describing what I described as a method that I would have liked to have seen done.

So after many Years although I had no responsibility for the wiring on most systems [since 2005] I am reassured that both methods are acceptable - "Thanks".

Regards,

Chris
 
The regulations do indeed allow flex to be used as fixed wiring as long as it’s the heavy duty type unless the risk of damage during installation is low etc etc, types of flexes are given in bs en 59565-1
For more detail see regulation 521.9.1 page 126 of bs7671.

Hello Ian1981,

Thank You very much for the information.

Would you guess that if the Flexes that I have described were `BS Heat Resistant Butyl` it would be likely to be `Good Quality` / `Heavy Duty` ?

I would never have known the specific BS / EN Numbers.

I would value your opinion please.

Regards,

Chris
 
Last edited:

Reply to Flex for fixed wiring in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock