Hi i have been asked to install a floodlight outside a garage. There is no DB in the garage but there is a flourescent. What would i have to do to pick up a feed for the floodlight? The flourescent is the only way i can see of getting a feed.
I would be greatful for any help.
 
you would only be adding a light and switch to an existing lighting circuit. if a 500w flood, that's 2 more amps, so could overload MCD. Prefer to feed from socket ring/radial via FCU if possible. perhaps a low energy flood would get you out of the proverbial
 
Last edited:
The floodlght will have a PIR aswel. Could anyone please descripe the best posible way for me to do this. i am currently an apprentice so have a little experience. just want to make sure i do it right. many thanks
 
best way is from socket circuit,( ring or radial) through fused spur. 1. it can be isolated. 2. It's fused down to 5A. 3.It complies with regs. 4. On most PIR floods, the fused spur can be used to manually override the PIR by flicking OFF/ON
 
Not Quite. You MUST bring out same size cable as the socket is wired in ( usually 2.5) to your spur, then 1.5 or 1.0 from spur to flood
 
also, any cable installed below 2metres or where it may be prone to mechanical damage must be protected. eg mini trunking
 
and don't forget to replace the 13A fuse in the spur with 3A or poss. 5A and mark the fused spur accordingly
 
debatable. as i see it, its same as adding an extra point to existing circuit.
 

Reply to Floodlight being installed in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, I have a single switch in my garage to turn on a couple of lights in there. Yesterday I fitted a floodlight outside, drilled through...
Replies
13
Views
2K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
553
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
687

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock