Discuss Flying leads and the regulations. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

steve snakeman

can anyone tell me where in the 17th edition it tells you in black and white that you do not need a flying lead attatched to metal back boxes from a socket.Also the same for a steel sink in a kitchen.I have been reading it all day and have a sore head.Thanks.
 
more to the point, where does it tell you that you have to bond kitchen sinks? sinks are not exranneous conductive parts unless the waste is metallic, in which case, the waste would need bonding. and it was back in the 16th, around 2003, trhat the need for flying leads was dropped as long as there was 1 fixed lug on the backbox. however, myself and a lot of other sparks prefer to fit a fly lead, if only to ensure that the backbox is earthed if the faceplate screws/pins are removed.
 
Thanks for the reply.I am aware of all of the above and also put in a flying lead however I have been asked to a meeting on Monday where I have to prove my point .Another electrician tested a collegues work where no flying leads were present and listed them as class 1 faults on his condition report.I defended my partners work by explaning this and have been asked to prove it :(
 
This is on the ESC website.

I would love to see what other code 1 observations were made if he classes this as Danger present Risk of injury.

So what did he do to elimanate that risk????????
SOCKET-OUTLET(S)SS181-5
Earthing of enclosure (back box)
Contents
1. Introduction

2. Where the cpc is a single-core cable or a core of a cable, connected directly into the earthing terminal of a socket-outlet
2.1 Metallic box with two fixed (non-adjustable) lugs
2.2 Metallic box with two adjustable lugs
2.3 Metallic box with one fixed and one adjustable lug

3. Where the cpc is formed by metallic conduit, trunking or ducting, or the metal sheath or armour of a cable


1. Introduction
Guidance is provided in this topic on whether it is necessary to install a so-called ‘earthing tail’ between a socket-outlet and an associated metallic back box. The guidance applies where protection against electric shock is by automatic disconnection of supply, as it is in the vast majority of cases.
A metallic back box for a surface-mounted socket-outlet is an exposed-conductive-part, and a metallic back box for a flush-mounted socket-outlet is deemed to be an exposed-conductive-part (even though it may not be able to be touched). Therefore, such back boxes, no less than every other exposed-conductive-part, are required to be earthed in accordance with Regulations 411.4.2 (TN systems) and 411.5.1 (TT systems) of BS 7671.
However, depending upon certain characteristics of the circuit protective conductor (cpc), the socket-outlet and its box, an ‘earthing tail’ may or may not be required between the socket-outlet and back box.

2. Where the cpc is a single-core cable or a core of a cable, connected directly into the earthing terminal of a socket-outlet
An earthing tail may not be required where the cpc associated with the circuit wiring from a distribution board to a socket-outlet takes the form of a single-core cable or a core of a cable, and is connected directly to the earthing terminal of the socket-outlet.
Whether an earthing tail is required depends upon whether one or both of the lugs on the back box are adjustable (to permit the socket-outlet to be levelled), and upon the earthing strap and eyelet arrangement of the socket-outlet, as detailed in items 2.1, 2.2 and 2.3.




2.1 Metallic box with two fixed (non-adjustable) lugs
The provision of an earthing tail is not required between a socket-outlet having an earthing strap and either one or two eyelets, and metallic back box as shown in Fig 1 (although the fitting of an earthing tail is still desirable). The box can be considered adequately earthed through the earthing straps and eyelets of the socket-outlet and the fixing lugs on the box.

2.2 Metallic box with two adjustable lugs
An earthing tail must be fitted between a socket-outlet and a back box having two adjustable lugs, such as the box shown in Fig 2. The need for this has been demonstrated where socket-outlets have suffered overheating and burning around the fixing holes due to a line-to-earth fault in metal boxes which had not been provided with an earthing tail. Because the adjustable lugs had become corroded, they presented a high resistance to the earth fault current, and consequently the circuit overcurrent protective device did not operate within the maximum time permitted by BS 7671. This resulted in a risk of electric shock as well as the thermal effects already mentioned.

Fig 1






Fig 2


2.3 Metallic box with one fixed and one adjustable lug
Care must be exercised when installing back boxes having one fixed lug and one adjustable lug, as shown in Fig 3, because some socket-outlets have only one earthing strap and eyelet. It must be ensured that the earthing eyelet is located at the fixed lug position, otherwise an earthing tail must be provided.
Photograph courtesy of Legrand Electric Ltd.

Fig 3



3. Where the cpc is formed by metallic conduit, trunking or ducting, or the metal sheath or armour of a cable
Regulation 543.2.7 of BS 7671 requires an earthing tail to be fitted where the cpc associated with the circuit wiring from the distribution board to the socket-outlet is formed by metallic conduit, trunking or ducting, or the metal sheath or armour of a cable. The earthing tail must connect the earthing terminal of the socket-outlet to the earthing terminal incorporated in the associated back box (see Fig 4).



An ‘earthing tail’ is required where the protective conductor is formed by metallic conduit, trunking or ducting, or the metal sheath and/or armour of a cable

Fig 4

The purpose of the earthing tail is not to earth the back box but to earth the socket-outlet (by connecting it to the back box).
The earthing of the back box itself is reliant upon the metallic conduit, trunking, ducting, or metal sheath or armour of a cable, forming the cpc. The requirements of BS 7671 relating to the use of such parts of a wiring system as a cpc are discussed in Topic P157-7.

 
This is on the ESC website.

I would love to see what other code 1 observations were made if he classes this as Danger present Risk of injury.

So what did he do to elimanate that risk????????
SOCKET-OUTLET(S)SS181-5
Earthing of enclosure (back box)
Contents
1. Introduction

2. Where the cpc is a single-core cable or a core of a cable, connected directly into the earthing terminal of a socket-outlet
2.1 Metallic box with two fixed (non-adjustable) lugs
2.2 Metallic box with two adjustable lugs
2.3 Metallic box with one fixed and one adjustable lug

3. Where the cpc is formed by metallic conduit, trunking or ducting, or the metal sheath or armour of a cable


1. Introduction
Guidance is provided in this topic on whether it is necessary to install a so-called ‘earthing tail’ between a socket-outlet and an associated metallic back box. The guidance applies where protection against electric shock is by automatic disconnection of supply, as it is in the vast majority of cases.
A metallic back box for a surface-mounted socket-outlet is an exposed-conductive-part, and a metallic back box for a flush-mounted socket-outlet is deemed to be an exposed-conductive-part (even though it may not be able to be touched). Therefore, such back boxes, no less than every other exposed-conductive-part, are required to be earthed in accordance with Regulations 411.4.2 (TN systems) and 411.5.1 (TT systems) of BS 7671.
However, depending upon certain characteristics of the circuit protective conductor (cpc), the socket-outlet and its box, an ‘earthing tail’ may or may not be required between the socket-outlet and back box.

2. Where the cpc is a single-core cable or a core of a cable, connected directly into the earthing terminal of a socket-outlet
An earthing tail may not be required where the cpc associated with the circuit wiring from a distribution board to a socket-outlet takes the form of a single-core cable or a core of a cable, and is connected directly to the earthing terminal of the socket-outlet.
Whether an earthing tail is required depends upon whether one or both of the lugs on the back box are adjustable (to permit the socket-outlet to be levelled), and upon the earthing strap and eyelet arrangement of the socket-outlet, as detailed in items 2.1, 2.2 and 2.3.

2.1 Metallic box with two fixed (non-adjustable) lugs
The provision of an earthing tail is not required between a socket-outlet having an earthing strap and either one or two eyelets, and metallic back box as shown in Fig 1 (although the fitting of an earthing tail is still desirable). The box can be considered adequately earthed through the earthing straps and eyelets of the socket-outlet and the fixing lugs on the box.

2.2 Metallic box with two adjustable lugs
An earthing tail must be fitted between a socket-outlet and a back box having two adjustable lugs, such as the box shown in Fig 2. The need for this has been demonstrated where socket-outlets have suffered overheating and burning around the fixing holes due to a line-to-earth fault in metal boxes which had not been provided with an earthing tail. Because the adjustable lugs had become corroded, they presented a high resistance to the earth fault current, and consequently the circuit overcurrent protective device did not operate within the maximum time permitted by BS 7671. This resulted in a risk of electric shock as well as the thermal effects already mentioned.

Fig 1


Fig 2


2.3 Metallic box with one fixed and one adjustable lug
Care must be exercised when installing back boxes having one fixed lug and one adjustable lug, as shown in Fig 3, because some socket-outlets have only one earthing strap and eyelet. It must be ensured that the earthing eyelet is located at the fixed lug position, otherwise an earthing tail must be provided.
Photograph courtesy of Legrand Electric Ltd.

Fig 3



3. Where the cpc is formed by metallic conduit, trunking or ducting, or the metal sheath or armour of a cable
Regulation 543.2.7 of BS 7671 requires an earthing tail to be fitted where the cpc associated with the circuit wiring from the distribution board to the socket-outlet is formed by metallic conduit, trunking or ducting, or the metal sheath or armour of a cable. The earthing tail must connect the earthing terminal of the socket-outlet to the earthing terminal incorporated in the associated back box (see Fig 4).
An ‘earthing tail’ is required where the protective conductor is formed by metallic conduit, trunking or ducting, or the metal sheath and/or armour of a cable

Fig 4

The purpose of the earthing tail is not to earth the back box but to earth the socket-outlet (by connecting it to the back box).
The earthing of the back box itself is reliant upon the metallic conduit, trunking, ducting, or metal sheath or armour of a cable, forming the cpc. The requirements of BS 7671 relating to the use of such parts of a wiring system as a cpc are discussed in Topic P157-7.

trust the esc to turn a simple 4 line explanation into an essay
 
just togive you a laugh I have been looking through his condition report and have just noticed this.....Hole in the wall where an extractor fan used to be ....requires further investigation?? That made me laugh.
 
very interesting, a regulation that condones skimping, can anyone tell me what is achieved by not fitting a fly lead, apart from the saving of 100mm of copper and a bit of sleeving. I am really glad that I am not working day to day in domestic any more!
 
very interesting, a regulation that condones skimping, can anyone tell me what is achieved by not fitting a fly lead, apart from the saving of 100mm of copper and a bit of sleeving. I am really glad that I am not working day to day in domestic any more!

About 3 mins labour per socket.

"Not much" I hear you say but when you're second fixing 30 dso's on a rewire, that's still two hours you could be spending on something else!
 
If ever you are unsure about anything regarding earth connections always fit more than less. I have personally seen someone crossbond radiators and sinks in bathrooms when they know that the pipes under the floor are PVC fed. ****ing madness!!! I personally as a joke charged one of these radiators with a wind up generated high voltage (MEGA) and got a teenager to touch the radiator which was cross bonded (to pvc supply pipes). He jumped as high as the red bull he had been drinking prior to shock and seemed alert and even more keen & inquizitive to learn about electricity after his short sharp shock. Once i explained about the 17th edition regulations he said "well that clearly does not make any sense then, i'm back on my X-box". I personally cover everything i use in bathrooms with SELV and RCD or RCBO. "radiators do not need bonding but cross-bonding to all copper or metal fed piping & metal bathroom furniture"
Contact [email protected] for any chats...
 
543.2.7

" Where the protective conductor is formed by METAL conduit, trunking, or ducting or the metal sheath and/or armour of a cable, the earthing terminal of each accessory shall be connected by a separate protective conductor to an earthing terminal incorporated in the associated box or other enclosure"

I underlined and made bold the only change from the original BS 7671.

So as to the regs the only time you need a fly lead in a box is when your using containment/exposed conductive part as protective conductor.

So though all the bodies ESC/NICEIC/GN notes advise that if there is not a fixed lug you should fit a fly lead on a T+E back box, it does not actually say so in the regs, and so if you are doing an EICR and found a non fixed lug box without a fly lead, should you code it ...............it is after all guides and advice say you should?

What would you do, and if you code it what would be the code, and why, and to what regulation.
 
very interesting, a regulation that condones skimping, can anyone tell me what is achieved by not fitting a fly lead, apart from the saving of 100mm of copper and a bit of sleeving. I am really glad that I am not working day to day in domestic any more!

I regularly nowadays come across back-boxes with one adjustable lug with no provision for a fly and they are passed to BS so I guess that says it all. Personally I fit them as a matter of course but Ive heard arguments saying you are more likely to create a problem by having 3 x cpc going into the earth on the back of a socket as its more likely to pull out than having 2. No way its a 1 on a PIR though, thats bonkers
 
The above qouted is actually(or appears to be) guidelines, not regulations. The guidelines say that in certain circumstances, the tail can be omitted, and goes on to list those circumstances. Unfortunately it is very flawed. this statement:

"The guidance applies where protection against electric shock is by automatic disconnection of supply, as it is in the vast majority of cases"

made me laugh out loud, as RCD protection is by no means universal. It may exist in the "vast majority" of new buildings. but in the rest it is simply not there! The "vast majority" of the domestic and commercial properties I enter are over 15 years old, and generally still use rewirable fuse protection.

Basically what it says is you can omit a flylead if one of the socket front fixing lugs is fixed, or the box is earthed by SWA or metal conduit and a seperate earth or cpc is connected to the socket front, BUT ONLY IF THE WHOLE IS RCD PROTECTED!!
However, take the situation where some scumbag hasn't used a grommet in a metal box and the insulation is damaged. When sparky looking for a fault comes along and removes the socket front ,fault clears because the only earth on the box is via the screw, but the box remains live when he restores power to give the sparky a belt when he comes back to it! As I have said in my earlier post ommiting flyleads is just skimping. As professionals , and I am now speaking to the time served properly qualified amongst us, we are supposed to use the IEE regs plus our common sense and experience to produce an installation that is safe in all circumstances. If you need a regulation to back up everything you do,and look for regulations that justify doing less than what will be safe in every circumstance, you are not fit to call yourself an electrician
 
very interesting, a regulation that condones skimping, can anyone tell me what is achieved by not fitting a fly lead, apart from the saving of 100mm of copper and a bit of sleeving. I am really glad that I am not working day to day in domestic any more!
Personally I don't do it, never have, if BS7671 reckons it's safe, I'll go with that.

The fact is, as long as the faceplate is fitted correctly, the backbox is going to be earthed by the screws, if the plate is off, then the installation is not in a safe completed state anyway and anyone unscrewing a live faceplate should realise this and realise that if the live wire jumps out (which it won't) and lands on the now unearthed backbox, said box will give them a belt. If they don't realise this and they get a belt, well, they'll know for next time.

Fact is I do good work, I use gromets, do my screws up properly, always have RCD protection (in houses) etc one of my backboxes isn't just going to magically become live and kill someone.

For me, time is money, I work for myself I'm always busy, rarely get away from a job before 5pm and anything that can save me time without breaking rules or affecting finished quality, I embrace.
 
Last edited by a moderator:
Fair enough Dave 85, but if you re read my post you will see that I describe the conditions where the back box will be live, and it does not involve any wires jumping out. Some ppl will put up with a lowering of safety standards, some will not. I rarely if ever go back to my own work, it is usually the work of others that causes problems, and that is also the place where accidents happen to unwary sparks!
 
Incidentally, Dave 85 if you NEVER do it, you are probably breaking guidlines in certain circumstances. BS7671 does not say you never need to fit a fly lead, it tells you under which circumstances you may omit a flylead. If the box has no flylead terminal, perhaps you are buying the wrong boxes for the circumstances, and perhaps this lowering of safety standards has been brought about by manufacturer lobbying in order to make box manufacture cheaper:)
 

Reply to Flying leads and the regulations. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
889
Does anyone else get emails and phone calls from companies and agencies say we seen your CV and we want you to apply for our job. And when you...
Replies
4
Views
607
  • Article
Electrical2Go - A Guide to Click Sockets: Which Is Right For You? Click Sockets Guide: Which is right for you? Click is a leading manufacturer...
Replies
0
Views
521
hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
Replies
6
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
746

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock