Discuss Flying leads and the regulations. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Sorry, but 2.5mm² will not be acceptable as a bonding conductor.
6mm² is the minimum, and where PME conditions apply, 10mm² is the minimum.
However, I would also suggest you determine the requirements of your supplier, as they may require 16mm².
 
This actually illustrates the problem very clearly There should be ONE set of rules which everyone works to. It used to be the IEE regs which had only one "current" edition which encompassed everything electrical, we now have a hopeless mish mash of guidlines ammendments and explanatary notes issued by organisationd which are actually in financial competition with one another, oh boy am I glad to be out of it after 40 years!!

There is one set of rules bs7671 2008 amendment 1!

As for there is no difference for earthing and bonding.....
Your on your own there.

Some people simply just won't listen

Cheers and gone
 
quote_icon.png
Originally Posted by hermetic

This actually illustrates the problem very clearly There should be ONE set of rules which everyone works to. It used to be the IEE regs which had only one "current" edition which encompassed everything electrical, we now have a hopeless mish mash of guidlines ammendments and explanatary notes issued by organisationd which are actually in financial competition with one another, oh boy am I glad to be out of it after 40 years!!

As said by Rich.250, there is only one "current edition" and each new edition is issued because of improvements for safety. Things change, even the IEE. Isn't it the IEEE now?
 

Reply to Flying leads and the regulations. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
884
Does anyone else get emails and phone calls from companies and agencies say we seen your CV and we want you to apply for our job. And when you...
Replies
4
Views
604
  • Article
Electrical2Go - A Guide to Click Sockets: Which Is Right For You? Click Sockets Guide: Which is right for you? Click is a leading manufacturer...
Replies
0
Views
513
hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
Replies
6
Views
1K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
742

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock