Hi all,

I recently bought a new house and I went to check the installation on my garage. There is a double socket and a fused switch (3A) which is connect to the light. When I opened this fused switch, I noticed it is actually a spur.

The way it is wired is that a SWA spur coming from the house is directly connected to the double socket and the same SWA goes through the fused switch to the light bulb (this is what I think sorry if I am not wording this with the proper terms).

Another thing I found is that I have all the ground floor sockets (kitchen, living room, bathroom, hallway) plus boiler plus garage all in a single 32 circuit.

My question is: Is this installation in accordance with the UK regs?

Thank you


IMG20221112143424.jpg
photo_6014776286012095172_y.jpg
photo_6014776286012095180_y (1).jpg
 
Although having 1 ring circuit for the whole house isn't ideal, it's very common in older properties and unlikely ever to be overloaded anyway. As for the spur off the spur, if its just a light it's unlikely to be an jssue.
 
How “new” is the house? New build or just new to you?

Agree that technically a spur from a spur shouldn’t be done.

3 storey house? Unless the top is a later loft conversion, they could have designed the installation a lot better.
 
Are you thinking, as it comes from circuit 5, it might be able to be put on a spare way as a radial?

Wider photo of the consumer unit might show it.
Yes, it could be a radial direct from the mcb rather than a spur, it would make more sense to terminate the swa there than off some point on the rfc.

And as swa could be suitable for protection by 32a
 
If you take the view that the double socket (20A) could be two single sockets (26A) then the double and 3A spur (23A) is unlikely to be an issue in reality.
A spur off a spur is advised against but not banned outright in the regs if the current is unlikely to exceed 20A (think I remember that right, it’s a bit early)
I wouldn’t be losing sleep over this particular one, especially if it’s an LED light bulb.
 
Just an observation, and not a steadfast rule either, but I wouldn’t have ground floor sockets and lights on the same RCD. Ground floor sockets with upstairs lights… and vice versa.

That way, if an RCD trips, you can have lights on somehow throughout the house either from ceiling lights or plug in table lamps.
 
Thank you for all your replies !

How “new” is the house? New build or just new to you?

Agree that technically a spur from a spur shouldn’t be done.

3 storey house? Unless the top is a later loft conversion, they could have designed the installation a lot better.

It is a brand new build, 3 storey.

Where dies the actual cable to the garage come from, is it direct from the consumer unit (fusebox) or somewhere off the house wiring?

It comes from the sockets by the TV in the living room. I have a picture of the house before the drywalls and I can see it written there "Garage Spur". So pretty sure it is not coming from the consumer unit.

Just an observation, and not a steadfast rule either, but I wouldn’t have ground floor sockets and lights on the same RCD. Ground floor sockets with upstairs lights… and vice versa.

That way, if an RCD trips, you can have lights on somehow throughout the house either from ceiling lights or plug in table lamps.

Yes, I've been told that. What is frustrating is that, being a new build, they had all the availability for doing this much better.


If you take the view that the double socket (20A) could be two single sockets (26A) then the double and 3A spur (23A) is unlikely to be an issue in reality.
A spur off a spur is advised against but not banned outright in the regs if the current is unlikely to exceed 20A (think I remember that right, it’s a bit early)
I wouldn’t be losing sleep over this particular one, especially if it’s an LED light bulb.

Thanks. Mostly I wanted to know if this is allowed in the regs, since the builders are still on site and I could ask them to change it to comply with the regs.
 

Reply to Found a spur on a spur (I think) in my garage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
449
I've had a search, and found an old thread from 2016... but was wondering about modern views on this situation. I've come into possession of...
Replies
5
Views
371
Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
218
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
901
Looking at instructions for installation for Baumatic BHI300 it requires a 20A Double pole (3mm separation) switched fused spur, I quote pretty...
Replies
3
Views
792

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock