Discuss Frost protection on combi boiler in the Central Heating Systems area at ElectriciansForums.net

Reaction score
145
Quick hypothetical question,

Combi boiler in garage with frost stat and pipe stat on return pipe, two zone valves for upstairs and downstairs, does the frost stat have to open one of the valves or just fire the boiler? Do they have a bypass valve?
 
I understand that but can it circulate water without opening the valves, as your only wanting the pipes to get hot?
 
So would I , it will depend whether you just want the boiler protected , ie located in a garage , or if the system is at risk from frost too - all depending on the/your location.
 
How old is the boiler??

There isn't one, I was just wondering as I've seen it done on new boilers, but they did not open the valves as far as I know so they must have an internal bypass?
 
A frost stat on the boiler is intended to protect the boiler from frost damage. A A stat internal to the property will independently fire up the boiler if it detects a risk of frost within the house for instance I.e. Opening up valves.

In answer to you question - just fire up the boiler.
 
A frost stat on the boiler is intended to protect the boiler from frost damage. A A stat internal to the property will independently fire up the boiler if it detects a risk of frost within the house for instance I.e. Opening up valves.

In answer to you question - just fire up the boiler.

However the heat from the boiler needs to go somewhere,
 
Dave, the boiler will heat up until the frost stat upper limit is satisfied. If the heat can't go anywhere all the better.

if the heat can't go anywhere the boiler will overheat and lock out, a modern boiler is too well insulated to leak enough heat to warm up the surrounding air and operate the frost stat. A pipe stat is required in series with the frost stat and fitted to the return pipe to the boiler.
Also when the boiler fires the pump will run, if the heat can't go anywhere then it will be pumping against the closed valves, hardly an ideal situation.
 
Seem to recall some manufacturers have an internal frost protection, Worcester Bosch Greenstar for example;

'The boiler has inbuilt frost protection. When the primary temperature drops below 8°C the pump is switched on. When then temperature rises above 9°C the pump switches off after a 3 minute pump overrun. If the primary temperature drops below 5°C, a central heating demand is activated until the primary temperature rises above 12 °C. The demand switches off followed by the pump after a 3 minute overrun.

The boiler has the facility to connect an external frost protection device to protect in “at risk areas” (terminal block ST6, contacts FS and FR). This is used if the boiler is not located in the area needing protection i.e. boiler in kitchen but pipe work in the garage that needs frost protection.
If external frost thermostat is calling, i.e. temperature within frost thermostat below the set point, but the primary temperature of the boiler is above 5°C, the pump will run until the temperature within the frost thermostat rises above the set point. If external frost thermostat is calling and the primary temperature is below 5°C, a central heating demand is activated until primary temperature is above 12 °C. If the frost thermostat is still calling the pump will run until the temperature within the frost thermostat location rises above the set point'.

The internal pump operates an internal bypass valve, when frost protection is required (8-5'), or CH demand (using external valves etc) when below 5', or so I believe.

So hypothetically, if the boiler was in a garage, with short lagged pump runs, just the internal frost protection could be relied on.

Edit: If you are looking to do such an install, can I suggest you consult a competent plumber, gas safe registered to install your new boiler :)
 
Last edited:
Seem to recall some manufacturers have an internal frost protection, Worcester Bosch Greenstar for example;

'The boiler has inbuilt frost protection. When the primary temperature drops below 8°C the pump is switched on. When then temperature rises above 9°C the pump switches off after a 3 minute pump overrun. If the primary temperature drops below 5°C, a central heating demand is activated until the primary temperature rises above 12 °C. The demand switches off followed by the pump after a 3 minute overrun.

The boiler has the facility to connect an external frost protection device to protect in “at risk areas” (terminal block ST6, contacts FS and FR). This is used if the boiler is not located in the area needing protection i.e. boiler in kitchen but pipe work in the garage that needs frost protection.
If external frost thermostat is calling, i.e. temperature within frost thermostat below the set point, but the primary temperature of the boiler is above 5°C, the pump will run until the temperature within the frost thermostat rises above the set point. If external frost thermostat is calling and the primary temperature is below 5°C, a central heating demand is activated until primary temperature is above 12 °C. If the frost thermostat is still calling the pump will run until the temperature within the frost thermostat location rises above the set point'.

The internal pump operates an internal bypass valve, when frost protection is required (8-5'), or CH demand (using external valves etc) when below 5', or so I believe.

So hypothetically, if the boiler was in a garage, with short lagged pump runs, just the internal frost protection could be relied on.

Edit: If you are looking to do such an install, can I suggest you consult a competent plumber, gas safe registered to install your new boiler :)

Indeed they do, but it's not every model of Worcester boiler which has this so you have to read the instructions every time.
 
Indeed they do, but it's not every model of Worcester boiler which has this so you have to read the instructions every time.

I can help the OP there, according to WB technical, only the CDI Regular hasn't internal frost protection. :)

But perhaps get a competent gas certified installer to read the instructions instead.
 
I can help the OP there, according to WB technical, only the CDI Regular hasn't internal frost protection. :)

But perhaps get a competent gas certified installer to read the instructions instead.

Well they could do with mentioning it in their installation instructions then, Somme of them mention it on the first couple of pages and others don't.
 

Reply to Frost protection on combi boiler in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

i , i have a property to work on which has a programmable room stat upstairs and a programmable roomstat downstairs. S plan system , 2 zones. hot...
Replies
5
Views
376
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
932
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
(Or that might be should a failed HW valve keep boiler running) Woke up this morning to find the boiler still running even though all timers off...
Replies
4
Views
1K
I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock