have been asked us to look at installing a different fuse as the 13A plug top keeps blowing when they try to start the Motor, its a very small bench compressor.

He seems to think it requires a fuse to allow the inrush of current, but the plate of the motor states its only 1500W so should this be blowing a 13A fuse on start up?

I cant see why it cant be hard wired in to a circuit with a 10A type C MCB instead?

Vac plate.jpg
 
Was it supplied with a plug top on it?
The starting current would exceed 13A.
I don't know what it is for single phase motors - I rarely deal with them - but for a three phase machine it would be typically be six times full load current or greater. We are given power (1500W) but not power factor or efficiency. So even running current could be close to 10A. Maybe the OP can shed some light on that.

In short, it doesn't surprise me that a 13A fuse blows.
 
That data plate looks like the plate from the compressor unit, not the plate from the motor.
I read that as being a compressor which requires a motor which can deliver 1.5KW of mechanical power.
Have a look at the data plate on the motor and see what that has to say.
 
That data plate looks like the plate from the compressor unit, not the plate from the motor.
I read that as being a compressor which requires a motor which can deliver 1.5KW of mechanical power.
Have a look at the data plate on the motor and see what that has to say.
The rating plate says 50Hz, must be referring to the motor rating.
The plate also gives compressor data.
 
I would not say that it is off a compressor, in fact I can almost be sure it is not a compressor.

Why are you all trying to apply BS7671 theories to machinery which is not covered by BS7671?

Again.
 
Infinity, your bench compressor will comfortably/safely run off a 10A Type C circuit breaker.
If it 'morphs' into a vacuum pump it will still be OK.
God help us.
 
Last edited:

Reply to Fuse Blowing on small motor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking for some guidance from more experienced hands. Have a friend who just bought a 2.2kw air compressor which is obviously blowing...
Replies
20
Views
4K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
Greetings everyone. My first post here, having read a similar thread, I understand that following the manufacturers guidance is all important...
Replies
10
Views
8K
How do you size the MCB, wire and protection for a motor in the UK/Europe? How is it typically done...
Replies
22
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock