aabbcc112233

hi there

my downstairs lighting ring fuse blows randomly sometimes instantly sometimes in 10 to 20 mins. ive tried a multimeter continuation test to see if there is any contact between earth and live and neutral and live on that circuit . which there doesn't seem to be.

there is continuity between earth and neutral . this is also at the consumer box . only this fuse blows. ive tried opening up sockets and checked them for any obvious signs as well as light roses as well.

its driving me crazy.

cant seem to find the fault

any help on how to find the problem will be much appreciated. by the way the fuse first blew in the middle of the night.
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

hi there

my downstairs lighting ring fuse blows randomly sometimes instantly sometimes in 10 to 20 mins. ive tried a multimeter continuation test to see if there is any contact between earth and live and neutral and live on that circuit . which there doesn't seem to be.

there is continuity between earth and neutral . this is also at the consumer box . only this fuse blows. ive tried opening up sockets and checked them for any obvious signs as well as light roses as well.

its driving me crazy.

cant seem to find the fault

any help on how to find the problem will be much appreciated. by the way the fuse first blew in the middle of the night.

Do you mean switches??
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

Sorry to state the obvious, but call in a local electrician:smile:
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

time to get a sparks in with the relevant test equipment to trace the fault. a multimeter will not find the fault unless it's a dead short, and even then, doubtful. imago's in your neck of the woods.
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

Water ingress, heat damage, rodent damage, knackered cables, knackered accessories.

One of the above probably.
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

A spark with the correct test gear will locate the fault bud.. Just bite the bullet get some that can find the fault..
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

I'm not far if you need a spark to take a look

have you got any outside lights on the circuit or done any DIY recently
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

no outside lights and no diy done recently mate

Then it could be a number of things.. Sedgy 34 is local.. Get in contact with him.. With the right test gear it will narrow down what the fault is..
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

So a fault has just developed??? Can you post a pic of what's tripping in the distribution board
 
I see you're a student electrician. but yet you got sockets and switches mixed up. lol!
sedgy34 is obviously near to you.best get him in and mebbe watch him as he pinpoints the fault. you may learn something..!
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

second white fuse wire from the right keeps blowing. have to replace it with 5 amp fuse wire each time

20130122_201322.jpg
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

If its taking out a rewirable then its overload or dead short.. Unless you can pin point it to a persific light or switch then without a tester then its trial and error..
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

If it taking out a 3036 it a wonder you cant see or hear where the fault is
 
Im sure a man of your caliber can have it traced+rectified all within a few hours Sedgy. maybe even give him a cheeky discount for being a member on here...
 
Re: fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me n

you will get continuity between neutral and earth,unless you isolate the board,this is due to neutral and earth being connected at transformer,please note this will not apply if TT system.
 

Reply to fuse blowing randomley somtimes instantly sometimes in 10 to 20 mins driving me nuts in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hello, thank you. I am DYI. Our daughter has home built in the 60s with fused service panel. One fuse has started blowing ; when a new fuse is put...
Replies
3
Views
1K
Hello, I’m not an electrician and I have a question in relation to Dimplex Duo300n. Some background information: a couple of months ago I have...
Replies
34
Views
7K
Hi, ive added some outdoor led lights to the downstairs lighting circuit. there are a few 24v lights which are powered by 3 x led drivers (15w...
Replies
28
Views
3K
Hi guys, first time poster, be easy! I'm caring for a friend and last night while sleeping on the sofa-bed an emergency system that had lost...
Replies
44
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock