    I PAT tested a Hotpoint Iced Diamond fridge freezer RFAA52. The CE plate on the back said 150W but the moulded plug said 13Amp. I looked up the instruction book on the Hotpoint web site and it said 13amp. I left the 13 amp fuse in the plug but it just seemed to be wrong. I sent an email to Hotpoint to ask the reason but they said that they could not answer the question.
    so why does a 150W appliance need a 13amp fuse?
     
  2. KAS1
    Offline

    KAS1 Electrician's Arms

    Location:
    King's Lynn
    The fuse is not to protect the fridge, only the flex................
     
  3. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    motor star up current would pop a lower rated fuse.
     
    • Like Like x 2
  4. Marvo
    Offline

    Marvo Admin and gender confused Staff Member Admin

    Location:
    South Africa
    150watts may run an ammonia absorption fridge but if it's a fridge that has a compressor then I don't believe it only consumes 150watts.
     
  5. Geordie Spark
    Offline

    Geordie Spark Regular EF Member

    Get a gas powered fridge then you won't need fuses to confuse you.
     
    • Like Like x 1
  6. MDJ
    Offline

    MDJ Guest

    It must be a very small fridge. The average Fridge freezer is around 400 watts tick over power. When the compressor kicks in it can be 6 times that amount hence the 13 amp fuse.
     
  7. kenuk
    Offline

    kenuk EF Member

    Location:
    uk
    Had similar with a slow cooker, tesco said to follow manufacturers instructions as its a safety instruction - still not sure why on earth a less than 200w appliance would need 13 amp fuse - its a slow cooker, surely no surges etc.
     
  8. darkwood
    Offline

    darkwood Super Moderator Staff Member Moderator

    Location:
    West Yorkshire
    Welcome to the forum kenuk, please take note of the posting dates of any thread your responding to as this is a year old thread, in regards to the topic in hand, don't be confused with plug top fuses - they are there on a lot of occasions to give short circuit protection only and not overcurrent protection as many often assume (although they are used of O/L protection too dependent on the product). A products current rating alone cannot be used as an indication of plugtop fuse rating.
     
  9. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    2 years, darkwood, 2 years. andf i thought i was going senile. :shocked3:
     
    • Like Like x 1