Discuss Fused spur rating for electric underfloor heating in the Central Heating Systems area at ElectriciansForums.net

Reaction score
1
Builder installed 175w / sq metre in an area 6.7 x 3.5. What should the fused spur be rated at and should it have a contractor as well?

Am I correct in thinking it is drawing just over 17A therefore 13A fused spur is insufficient?

Thanks
 
Is the spur (aka FCU) getting warm? I would probably switch it off until you have got to the bottom of things.
 
6.7 x 3.5 = 23.45
23.45 x 175 = 4.1kW
4.1kW / 240 = approx 17A

Depending, as Mike said, whether this is mat size or room area.

OP, is the FCU ('spur') warm?
 
OP, is the FCU ('spur') warm?

ask when he's taken the washing off of it.
 

Reply to Fused spur rating for electric underfloor heating in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
Hi there I have a few questions related to the power ratings of certain devices and how this interplays with the fuse. The reason I am asking...
Replies
4
Views
991
Conversation developed with a middle aged lady who has recently lost her husband. Note to self, stop walking dog around the graveyard Anyway...
Replies
5
Views
1K
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
906

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock