Could you more experienced testers explain your working methods for the use of the three variants of leads used with a Multifunction tester ?

As I understand it to be GS38 compliant they have to be 500mA fused but this makes them unsuitable for loop testing as this adds a large resistance to the leads ( But can't this be nulled out ? ) So perhaps just for dead tests ?

The other option is the 10A fused leads which will offer short circuit protection but are not GS38 compliant

Or stick with non-fused and make sure I work with good safe working practise ?

Oddly the new Megger came with non-fused with the option to purchase the other.

Thanks for looking.
ATB Steve
 
A 500mA fuse in a lead will blow the moment you conduct a loop test, due to the large currents used for these, anywhere from about 9A to 25A. A 10A fuse is normally the way to go...

Personally though, I don't use fused test leads at all and apart from a few bangs and some very sorry looking probe tips I've never had a problem...
 
a 500ma fuse in a lead will blow the moment you conduct a loop test, due to the large currents used for these, anywhere from about 9a to 25a. A 10a fuse is normally the way to go...

Personally though, i don't use fused test leads at all and apart from a few bangs and some very sorry looking probe tips i've never had a problem...

:d:d:d
 
same here mate i have megger 1552 leads are not fused i was told they dont have to be as there is a 500mA in the tester when i asked about this was told it was fine without as thats how they are manufactured the fluke ones i used at college did have pain in the ? keep swapping fuse about when changing tips and clips for 2391 exam wish i had took my megger with me
I was thinking the same thing as GS38 states they should be so??? in answer to your question
 
I have unfused leads, GS38 compliant 500mA fused leads and 10A fused leads. And swap them about depending on what I'm doing.
 

Reply to Fuses lead/Unfused and GS 38 Leads in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I make my own ceeform adaptor leads for testing purposes where the 4mm banana leads generally just get plugged into my own MFT which is all...
Replies
3
Views
1K
I have an older house that was built in stages back around 1960 as far as I can surmise. Highly suspect that the entire house was a DIY job. I've...
Replies
1
Views
1K
Hi There, Just invested in a Fluke 1664FC multifunction tester in the hope of gaining accurate - repeatable results but unfortunately it's not...
Replies
35
Views
10K
Megger 1005-135 3 Wire Test Lead Set (Unfused) for MFT1552/MFT1553 Multifunction Testers New unused Genuine Megger £30 posted
Replies
0
Views
1K
Megger MFT1730 with Bluetooth. Calibrated until sept 2018: Used, but great condition. Comes with all accessories. Wanting £600 Ono Some spec...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock