Discuss Garden Heaters question. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi all I was at a job and an electrician was fitting 2 patio heaters.
They were fed by a 4mm armoured and were 2Kw each which was fine.
He was doing a nice neat job but I did notice that he cut the plugs off the heaters and terminated the flex straight into the adaptable box via a stuffing gland.
I asked about them now not being fused at 13A but he said they are going on a 20A mcb and each heater is only drawing a maximum of just over 8.5A which is ok?
Is it? or should there be either a socket for them to plug into or a fused connection unit?
I didn't question further as he was an older chap and seemed to have been doing his job longer than I've been around.
Your views/opinions on this would be appreciated thanks.
 
These are a resistive loads so no overcurrent but still need to check for shock protection (or whatever the correct phase is everytime regs change) disconnection time 0.4 sec you say it is a radial circuit 20A mcb what was the Zs as outdoors I would of put on RCBO.Where was these A.boxes put ?
 
These are a resistive loads so no overcurrent but still need to check for shock protection (or whatever the correct phase is everytime regs change) disconnection time 0.4 sec you say it is a radial circuit 20A mcb what was the Zs as outdoors I would of put on RCBO.Where was these A.boxes put ?

Thanks for the reply,
I didn't gather too much information as I was a little busy myself but I know the breaker was a 20A mcb on a split load rcd board.
The adaptable boxes were mounted on the wall about half way up then the heaters to the side and about a couple of foot above.
I will try and find out what the zs was.
Thanks
 
I see your point you was making regarding cutting off of the plugtop could of put into IP S.F.spur (local isolation/protection of flex etc) but as I posted resistive load so should have no overload as long as Zs within max permitted for mcb shock (sorry fault) protection met also additional protection by RCD as you have just stated.
 
Only thing I would say is a stuffing gland may provide some ingress protection but it does not provide suitable cord restraint, they are not designed for this although it is common practice.
 

Reply to Garden Heaters question. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
585
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
Replies
23
Views
4K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
879

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock