Search the forum,

Discuss Gas Bond Yes or No? in the UK Electrical Forum area at ElectriciansForums.net

J

James Croxford

I have just carried out an EICR and the only C1 defect I found was no 10mm bond to the gas. As this is not a fixed gas feed but only a gas cylinder I guess this still requires an earth bond from the DB? (feeds hob only)

My next question is, if the rubber hose from the cylinder was to continue in plastic all the way to the hob would it then be exempt from having to have an earth bond at the cylinder?

Here's a picture I took yesterday....










attachment.php
 

Attachments

  • 20131030_123008.jpg
    176.4 KB · Views: 203
Last edited by a moderator:
I have just carried out an EICR and the only Cat 1 defect I found was no 10mm bond to the gas. As this is not a fixed gas feed but only a gas cylinder I guess this still requires an earth bond from the DB? (feeds hob only)

My next question is, if the rubber hose from the cylinder was to continue in plastic all the way the hob would it then be exempt from having to have an earth bond?

Here's a picture I took yesterday....






Haha, very funny, from the wording it looks like you are asking do you need to bond a rubber or plastic pipe:lol:
 
The pipe work passes continuity (R2 lead test) as the hob is earthed through the fused spur. This would still be classed as an extraneous conductive part, correct?
 
The pipe work passes continuity (R2 lead test) as the hob is earthed through the fused spur. This would still be classed as an extraneous conductive part, correct?

That is not the correct method to determine if a service is extraneous or not apart from the need for a wander lead :)
 
The pipe work passes continuity (R2 lead test) as the hob is earthed through the fused spur. This would still be classed as an extraneous conductive part, correct?
No.

To test whether it is extraneous you must isolate the pipe (disconnect) and IR test it to the MET.
As you are doing an EICR and you will not want to do this perhaps you should assume that it was deemed not extraneous when fitted because it doesn't go to earth.

P.s. it is 'earthED (equipotential) bonding' not 'earth bonding' - subtle difference.
 
No.

To test whether it is extraneous you must isolate the pipe (disconnect) and IR test it to the MET.
As you are doing an EICR and you will not want to do this perhaps you should assume that it was deemed not extraneous when fitted because it doesn't go to earth.

P.s. it is 'earthED (equipotential) bonding' not 'earth bonding' - subtle difference.
but if he isn`t sure (visual)...then he proves it by means of IR & wander lead....doesn`t he...
 
Isn't that what I said?

He's doing an EICR.

No help doing an IR with it connected to the hob and CPC.

Would he test or be worried by an outside tap?
 
I have just carried out an EICR and the only C1 defect I found was no 10mm bond to the gas. As this is not a fixed gas feed but only a gas cylinder I guess this still requires an earth bond from the DB? (feeds hob only)

My next question is, if the rubber hose from the cylinder was to continue in plastic all the way to the hob would it then be exempt from having to have an earth bond at the cylinder?

Here's a picture I took yesterday....










attachment.php



I'm not sure about the regs. regarding LPG, but if this were Natural Gas and you ran it in plastic you would have you balls cut off - and rightly so !!

Running gas in properties through non-metallic pipework fell out of favour just after the Ronan Point disaster !! ( Google that one sometime! )
 
1. missing bonding is a C2 , as glenn correctly infered.

2. a gas bottle sat on the floor is not an extraneous part in any way and doesnt not require bonding , and neither does the pipe which isnt even touching the ground.

seems to me like some poor home owner has recieved a failed inspection to which they did not deserve , which is all down to p*ss poor understanding of basic principles.
 
The pipe work passes continuity (R2 lead test) as the hob is earthed through the fused spur. This would still be classed as an extraneous conductive part, correct?

James,
As the guys have already stated................bonding the pipework and the gas bottle would be the perfect example of 'introducing' a hazard by unnecessary bonding.
An earth fault on the system would /probably raise said pipework and cylinder to mains voltage(think aluminium double glazing in past years) and the poor sod that comes to change the bottle will be it's path to earth.........probably:)
 
here....
have a stug111:

View attachment 21237

or how about something classic:

View attachment 21238

Ah, the Sturmgeschütz III was a fine fighting machine, given the choice a brilliant selection for a tank commander to see through an ambush or a meeting engagement. The Jagdpanzer IV however with its better armour arrangement, longer range and faster speed made it a great weapon for blitzkrieg!

Personally however, with the freedom to choose from either side the tank I would most want to be in would have to be either a Hetzer or a Hellcat. Shoot and scoot is and always has been my MO!

Probably why I often like to bodge it and scarper :D
 
Ah, the Sturmgeschütz III was a fine fighting machine, given the choice a brilliant selection for a tank commander to see through an ambush or a meeting engagement. The Jagdpanzer IV however with its better armour arrangement, longer range and faster speed made it a great weapon for blitzkrieg!

Personally however, with the freedom to choose from either side the tank I would most want to be in would have to be either a Hetzer or a Hellcat. Shoot and scoot is and always has been my MO!

Probably why I often like to bodge it and scarper :D
well...

i prefer to stand there and fight it out:

the-first-battle-squadron-of-dreadnoughts-1910-L.jpg
 
What a beautiful piccie !!

I have one of a WW1 Dreadnought sailing down the Tyne on its way to its sea trials after being built at the famous Armstrong's works.

Bloody magnificent sight - all smoke, might and majesty. I'm reminded of Tidyboiler every time I see it.


I've got a painting of a cocktail sausage......................... I'm reminded of Geordie........................ ;)
 

Reply to Gas Bond Yes or No? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
2K
What are the regulations requirements on Earth bonding ? I am currently planning a 1st fix re wire I have the following setup Gas Meter...
Replies
3
Views
2K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
324

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock