Reaction score
17
When doing mock exams 17th edition the questions that always have me stumped are about general characteristics, I had a question with maximum demand and max current in choices, both seemed feasible answers
 
Maximum demand is generally the figure you obtain after diversity is applied to the maximum current. For example if you have three 32A ring final circuits their maximum current demand could theoretically be 96A but in reality this is not likely to happen so you apply diversity to come up with a maximum demand figure.
 
Right so what they are looking for is a design figure not an absolute, but in characteristic of design max current would be a consideration to arrive at max demand
 
Heres another strange one
7 o/c 4 - Which of the following items does not offer ‘basic’ protection:
a a circuit protective conductor.
b a socket outlet.
c a lampholder.
d equipotential bonding conductors
 
If a fault occurs in the HV system and a magnitude of fault voltage of 430v occurs between exposed conductive parts and earth on the LV installation, what is the maximum tolerable duration of the fault
 
If a fault occurs in the HV system and a magnitude of fault voltage of 430v occurs between exposed conductive parts and earth on the LV installation, what is the maximum tolerable duration of the fault

Have a look at Reg 442.2.2 mate
 
25) If a fault occurs in the HV system and a magnitude of fault voltage of 430v occurs between exposed conductive parts and earth on the LV installation, what is the maximum tolerable duration of the fault
a) 10ms
b) 100ms
c) 200ms
d) 300ms

I don't know how to answer this one
 
Last edited:
What needs to happen generally under fault conditions, disconnection (ADS). You are looking for disconnection times.
 

Reply to General characteristics in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Sticky
Everyone loves food! So to stop always hijacking the good morning thread I've made our own place to chat and drool about food! Recipes, photos or...
Replies
22
Views
602
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
600
Hello all Well, been putting it off, but I need to upgrade my 17th edition to the 18th. Not been a practising sparky for over 5 years, but I have...
Replies
19
Views
1K
Hello all Planning to do the 18th edition online. I could just batter loads of old papers on the head and then have an attempt ( I will do loads...
Replies
11
Views
1K
Hi Folks , Just looking for a bit of advice as I'm looking to get back on the tools so please bare with me if this is a bit long winded. I'm a...
Replies
1
Views
613

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock