surely, if you were to cut off the plug you would connect to a FCU, not to an unfused outlet.
surely, if you were to cut off the plug you would connect to a FCU, not to an unfused outlet.
Here is a paragraph from the On site guide
Permanently connected equipment
Equipment should be locally protected by a fuse of rating not exceeding 13 amp or by a circuit breaker of rating not exceeding 16amp
and should be controlled by a switch where needed
A separate switch is not required if the circuit breaker is to be used as a switch
The above comes from the section headed Final circuits using socket outlets complying with blah blah
The whole section seems to trip over itself with clarity
The point a few of us were making is that "Manufacturers instructions" overrules that. If an appliance states that "must be protected by a 13 amp fuse", then that is what you have to do.