Hi everyone,

I have been given the job of installing twelve 70w SON-I light fittings to light up an equestrian arena. The arena is in the middle of a field nowhere near an electrical supply. Therefore we are going to use a generator. The question I have is twofold. Firstly what size of generator should I use to allow for starting current of the SON lamps. Would 2 KW be sufficient?

Secondly, what about the earthing arrangement? I presume a TT arrangement would be in order, but how would I do this? The generator will also be a mobile type, that will be moved in and out of a shed. The arena is not covered.

Any help will be appreciated.
 
What type of generator?

A site generator is no use for a permanent installation.

As for the earthing a good earth rod needs to be driven and linked to the neutral output. This will give a TNS system.

As for the start up load, if you switch all the lamps at the same time, you’re going to pay the cost. Staggering the start up then you don’t need much more than the loading.
 
Come on Dolph, are you just trying to get into character.? Sherley, its for some amazingly exciting movie about electricians, that get attacked by fanatical NICEIC terrorists, who must try to destroy BS7671 before part P is exposed for what it is, a shameful scam aimed at 5 week wonders and Muslims before America and the good old US of A is destroyed...wow what a movie I just hope the commies dont get involved.
 
Come on Dolph, are you just trying to get into character.? Sherley, its for some amazingly exciting movie about electricians, that get attacked by fanatical NICEIC terrorists, who must try to destroy BS7671 before part P is exposed for what it is, a shameful scam aimed at 5 week wonders and Muslims before America and the good old US of A is destroyed...wow what a movie I just hope the commies dont get involved.


Been out at the pub tonight? :29:

Boydy
 
Hi everyone,

I have been given the job of installing twelve 70w SON-I light fittings to light up an equestrian arena. The arena is in the middle of a field nowhere near an electrical supply. Therefore we are going to use a generator. The question I have is twofold. Firstly what size of generator should I use to allow for starting current of the SON lamps. Would 2 KW be sufficient?

Secondly, what about the earthing arrangement? I presume a TT arrangement would be in order, but how would I do this? The generator will also be a mobile type, that will be moved in and out of a shed. The arena is not covered.

Any help will be appreciated.

Hi Jean Claude :20::biggrinjester:

I know this is not what you have asked , but if it is going to be a standard size arena I think you may want to up rate them to at least 150w fittings , and although the Son-I fittings will give you a further reaching spread , the quality of light will be useless for any form of serious dressage work .
You may want to suggest metal halides , or at least make sure your client understands that the light will be the colour it is !?
 
Hi Jean Claude :20::biggrinjester:

I know this is not what you have asked , but if it is going to be a standard size arena I think you may want to up rate them to at least 150w fittings , and although the Son-I fittings will give you a further reaching spread , the quality of light will be useless for any form of serious dressage work .
You may want to suggest metal halides , or at least make sure your client understands that the light will be the colour it is !?

I doubt if any SON lighting system would meet official equestrian arena requirements either!! Most sporting events at arena's, pitch's fields etc are lit by metal halide lamps these days....
 
Thanks everyone. Just to let you all know that we are not allowed to use any white light (ie LED or Metal Halide) due to planning restrictions. The local authority specified 70w SON. Bizarre I know, but true. And it's not a proper arena, more of a horse type playpen for rich kids to run about.

Cheers guys.........
 

Reply to Generator query in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All Had an enquiry about installing a generator fed UPS to a house. I have a minimal amount of experience with UPS but am certainly no expert...
Replies
3
Views
1K
I know it's not neat, but can I simply run a single extension cable from a small (3KVA) petrol, portable, inverter generator, positioned outside...
Replies
14
Views
3K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
556
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi Everyone, I'm new to this forum and am hoping someone can give me some advice, as I'm absolutely clueless when it comes to these things. I'm...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock