Search the forum,

Discuss gland swa at both ends? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
16
Just wondering if others make off their armoured glands at both ends has have worked with sparks previously and seem to have different takes on it. My thoughts are that if glanded and so earthed at origin is acceptable so if for example supplying a sub board in garage a plastic gland at the board is fine and SWA glanded at origin of supply so house board is fine?
 
A gland at both ends provides additional cable restraint that a stuffing gland won't to the same level. Should always gland the supply side as a minimum in my opinion. Personally I would always gland both ends, even into a plastic db. Obviously if the armour is also used as CPC then there must be continuity somehow.
 
As above, plastic glands for TT isolation purposes.

Maybe other odd cases, such as small 3-core SWA in to an outdoor light where they did not really expect a metal gland or provide adequate space for one.
 
Regulation wise my memory tells me that the SWA should be glanded / earthed at at least one end and preferably the supply end.

I think this is why some people think that glanding at only one end is acceptable.
 
Regulation wise my memory tells me that the SWA should be glanded / earthed at at least one end and preferably the supply end.

I think this is why some people think that glanding at only one end is acceptable.
That's my point Ferg. I possibly understand the use of SWA gland for adding support to cable or using the SWA for earthing but in terms of an actual shock risk if cable aupported i fail to see one. A live conductor needs to come in contact with the steel sheathing and if this is earthed at supply end all good.
 
While it is not a common electrical requirement as such, if you correctly terminate the outer screen to the metal work where a cable enters by a gland or connector providing 360 deg contact as you get much better screening of high frequency noise from a EMC perspective.

In power systems this is only likely to be lightning surges, but it is a far more critical requirement for coax cable where taking the braid/shield in as a "pig tail" is very bad news from a radio screening and constant-impedance perspective.
 
Why do you think swa glands come in packs of 2?

the right tools for the right job.
I think I've heard of them....do they come with an instruction pack?

IMG_0193.JPG

IMG_0189.JPG

IMG_0190.JPG
 

Reply to gland swa at both ends? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
I'm working on a system that has been installed incorrectly. It's a 3ph Hager board with 8 swa cables glanded into the bottom entry panel. The...
Replies
28
Views
3K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
785
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top