Discuss Grade A... fire detection/ domestic property !? in the UK Electrical Forum area at ElectriciansForums.net

sythai

-
Arms
Reaction score
356
Hi Guys

Recently finished a new build house, 2 levels/ 5 bed.
Wired AICO grade D LD2 system throughout.

LABC has come to sign off saying needs to be grade A system.
Havent got full details, just to chatted to builder (owner of property) on phone.

Did only think this was required on a domestic property when 3 levels+ and/ or HMO ?

Can someone help on this please ?

Thanks Sy
 
Sounds odd hopefully someone has crossed wires because a Grade A LD2 system will require a Part 1 control panel.
 
just got bit more info..... when footprint is >200sq meters then also grade A required.
This place is right on the limit of 200sq meters ! and we have pretty unhelpful labc inspector, which doesn't help things 🫤
 
Was an architect involved with this build? (sounding by the size of it, there should have been)

They should have known.... they get paid enough
Sure was…. Builder has now gone back to him.
Would have been helpful if LABC maybe brought this up on one of their site visits during 1st fix.
 
So what’s the solution? Does it have to be hard wired? Running cable surface? That’s going to look good in a finished build.

Is there a battery solution that can be used?

Hopefully the LABC are mistaken, but it’s going to be an uphill struggle to get them to admit it.
 
So what’s the solution? Does it have to be hard wired? Running cable surface? That’s going to look good in a finished build.

Is there a battery solution that can be used?

Hopefully the LABC are mistaken, but it’s going to be an uphill struggle to get them to admit it.
We've spoken to 'fire alarm co.' we use from time to time...... there is a wireless system that would do it and comply with LABC.
Will be pricey though !! Better than pulling £1.5million new build apart to hard wire (which isn't a conventional layout by any means)

Next step is back to LABC to try and negotiate, over to the Architect/ Builder
 
That’s what I mean about an architect.

If it was on the drawing to begin with, then someone on site isn’t reading the plans….
If it was passed by LABC without being in the plans, then LABC hasn’t read them.
wasn't stated on plans for this one.
footprint was 202m/sq... just over !
 
Does this just apply to new builds… or do same regs apply for a refurb also above 200 sq/meters? Thanks Sy
The rule must have been in place for some time, i remember coming across it on a farm house refurb with extension 15 years ago, property was only 2 floor house, but about 250 sqm so required a grade A system. Be interesting to see if its the architects fault or labc if it was or wasnt on the plans
 
Last edited:
Must admit, this one's new to me, and I've worked on loads of domestic properties over 200m2, mostly refurbs, but some new. It's not that big, when you're considering farm houses.
 
Wouldn’t be difficult to build a fake wall over a walk in wardrobe or something…. Wood frame, plasterboard… painted to match. And a lovely family portrait hanging… get it passed, then take it away.
 
Bit like the internal door building control wouldn't allow in my last barn conversion. Light switches in place both sides, lintel in place, and boarded across the opening both sides.
Wardrobe isn't habitable area anyway, AFAIK.
 
….. so outcome was!

Architect got on the case and floor space was recalculated using a ‘net’ value which subtracts all the internal walls. This brought it in under the 200msq

And all fine with grade D/ LD2.

Good news for everyone involved😉

(Existing LABC causing grief on all fronts has also been given the boot and new private BC brought in.)
 

Reply to Grade A... fire detection/ domestic property !? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So I've just recently qualified from my apprenticeship and I'm looking to expand my knowledge on a few different systems such as: A) CCTV B) Fire...
Replies
6
Views
1K
Hi all I have a small problem with a job im doing, 2 first floor flats above a shop with separate landlords area for the 2x flats which is a...
Replies
3
Views
2K
HMO property wants an annual periodic inspection cert for a grade D mains linked smoke alarm system. Far as I'm aware only installation and...
Replies
0
Views
1K
Hi, as the title says I've recently finished my Level 3 course, I'm based in Swindon but have my own car and I'm willing to travel up to roughly...
Replies
0
Views
885
Doing an eicr at a HMO property today and was asked to test/certificate for the smoke detectors which are aico mains powered interlinked alarms, i...
Replies
7
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock