Just wanted to see if the following is the correct way to supply a socket in a greenhouse.

Firstly the supply is tn-s and the customer wants a socket in the greenhouse for a heater. Now the supply to the greenhouse would come from the shed supply as it’s on a separate circuit. I was thinking of:

Run 2 core 2.5mm swa from shed cu to greenhouse using armour as earth in supply cable.
Terminated cable into ip rated double socket.
Insulate gland at greenhouse end and fit earth rod to give an earth due to bonding to the greenhouse.
Fit rod and run 10mm earth into socket and also bond greenhouse at same time.

Is this acceptable in regards to the bonding?
 
You first need to check if the greenhouse frame is an extraneous earth (under 23,000 ohms). You wouldn't need an earth rod in either instance. Hopefully the socket will be RCD protected at the shed supply?? If you do want to bond or earth this steel/allum' frame, run in a 3 core SWA and use the third core!! Bit different if it was a TNC-S, but as you say, this is a TN-S system!!
 

Reply to Greenhouse socket supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
645
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
346
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
929
A friend of mine wired a 10mm 3 core armoured cable to his shed before I got involved and wired it himself already. He wants make it an air bnb...
Replies
8
Views
910

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock