Nothing personal on you @daavvee , just due diligence, and probably a polite advert (to follow) to join our trainees section in a slightly 'less hostile' area of the forum.This is a private job that is then going to be tested and signed off. Any reason?
Indeed. However, the data sheet for Click Mini Grid Double Pole single module switches says they are 13 amp (resistive) ,10AX.Because dp switches come rated at 20A....
The Click Mode Mini Grid DP 13 amp rated switches come labelled with appliances like Oven, Washing Machine etc.Some grid switches are intended for lighting and 10A or so rated, others are 20A, typically the DP switches, so you do need to check the spec carefully!
Part of the problem I had was the stiffness of the 2.5 cable was twisting the switches out of the grid as you pushed it back into the box with similar problems if you need to remove it to replace a switch IMO using the minigrid created more problems than it solvedThe Click Mode Mini Grid DP 13 amp rated switches come labelled with appliances like Oven, Washing Machine etc.
Although I'm a big fan of the Click range in general, I am a little skeptical about the use of the Mini Grid switches for high load appliances.
I should I expanded more on the last sentence. Fusing is required, but this can be the fuse in a 13A plug, if the switch is connected to a single 13A socket, or a fuse in a SFC if the appliance is hard wired.Any 'fixed' appliance 2kW or over (in this example, the oven), should have its own dedicated supply from the CU.
Igniter and fridge/freezer are trivial loads, and wash/mac. is a high, but very intermittent load, so these three could come off of the existing RFC. They will need fusing downstream from the switches.