Discuss Groundwire sparked while connecting it to the main ground in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi all

So, my brother bought a (new to them) house. I've been redoing the fuse boxes in the house. Today, while putting the grounds from the kitchen together the last wire made a little spark... but the differential didn't trip so is this a big problem? Something to look into? Or something to disregard? All these grounds were wired together before I worked on it for at least a few years.

Also, the Ri was too low only 25kohm could that possibly be the problem?

Located in Belgium
 
Hi all

So, my brother bought a (new to them) house. I've been redoing the fuse boxes in the house. Today, while putting the grounds from the kitchen together the last wire made a little spark... but the differential didn't trip so is this a big problem? Something to look into? Or something to disregard? All these grounds were wired together before I worked on it for at least a few years.

Also, the Ri was too low only 25kohm could that possibly be the problem?

Located in Belgium
Firstly the "differential" (rcd) will only trip when's its rated leakage current is exceeded (30 ma). Any appliance which has intentional leakage in its design will "spark" if you disconnect or reconnect its circuit CPC but will not trip the rcd as the intentional leakage is designed to be much lower than the rcd rated tripping current. This is completely normal.
But to establish exactly what's causing the sparking it would be wise to trace exactly which circuit the sparking earth belongs to and trace exactly what it is connected to.
 
As above, a small spark is quite normal due to functional leakage from appliances and capacitive leakage from the cables, but really you should not disconnect any grounding cables or connections while any part of the system is energised. Even then, with the main switch off, there can be sparks between one 'version' of ground and another (e.g. between a buried metal water pipe and the electrical supply ground) due to externally-created potential differences. Especially if the supply is TN-C-S, where normal voltage drop in the earthed neutral creates local variations from 'true' ground.

So in short, a spark is not unusualy and does not always indicate a fault. Insulation of 25kΩ does indicate a fault and needs finding and correcting.
 

Reply to Groundwire sparked while connecting it to the main ground in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have breaker box at least 40 yrs old, both conduit and romex enter box, only one neutral bar that all white wires and bare ground wires attach...
Replies
4
Views
734
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
653
Hi all. This is my first post on here so hopefully some of you will be able to suggest something other than my ideas. Worked as a spark for 19...
Replies
16
Views
2K
Hello. I'll apologize to start with as due to my lack of knowledge on the matter I'm likely to waffle a bit and call everything by the wrong name...
Replies
16
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock