Thought id start a thread for posting those unusual faults that have you scratting your head for age, feel free to post one for a guessing game but here goes with mine....
Call out to a work yard who have a metal container cabin decked out with a few sockets and lights, the problem was nothing worked and they had checked mcb's and rcd's.
So just to clue you up and no i didnt wire it but this is how i found it... 180amp 3ph generator feeding a dist' board DB1 in an adjacent cabin- off this DB1 it also fed a small consumer unit in same cabin DB2, it was a front end rcd on this board and one of its outgoing circuits fed the steel container dist' board DB3 that was having problems.
First i check DB2 rcd and outgoing mcb were on --- yes
Then i opened DB3 and checked for voltage --- L-N Ov / l-E 230v / N-E 230v (note single phase board)
Next i checked the power in DB2 ... front end rcd L/N input 230v --- rcd output L/N 0v
rcd output to E was L/E 230v & N/E 230v
This rcd was in the on position what was my fault and why was i getting 230v N/E and L/E when i had switched off the mcb powering DB3 (note mcb was working fine)
Hope you took all that in lol
I just add for more confusion ... DB2 and DB3 had front end rcd's 30mA and the sockets off DB3 were RCD sockets....YEP!!! crazy :6:
Call out to a work yard who have a metal container cabin decked out with a few sockets and lights, the problem was nothing worked and they had checked mcb's and rcd's.
So just to clue you up and no i didnt wire it but this is how i found it... 180amp 3ph generator feeding a dist' board DB1 in an adjacent cabin- off this DB1 it also fed a small consumer unit in same cabin DB2, it was a front end rcd on this board and one of its outgoing circuits fed the steel container dist' board DB3 that was having problems.
First i check DB2 rcd and outgoing mcb were on --- yes
Then i opened DB3 and checked for voltage --- L-N Ov / l-E 230v / N-E 230v (note single phase board)
Next i checked the power in DB2 ... front end rcd L/N input 230v --- rcd output L/N 0v
rcd output to E was L/E 230v & N/E 230v
This rcd was in the on position what was my fault and why was i getting 230v N/E and L/E when i had switched off the mcb powering DB3 (note mcb was working fine)
Hope you took all that in lol
I just add for more confusion ... DB2 and DB3 had front end rcd's 30mA and the sockets off DB3 were RCD sockets....YEP!!! crazy :6: