page 122, 0 degrees has factor 0.96 table A6,and page 129 table B2 has 0 degrees at 0.92,
I understand that table A6 corrects from 10 degrees,and B2 from 20,but why not same value ,
 
Hi - reasons given in Note 2 page 122, because the starting points are different by 10 degrees, then the factors will be a little different.
 
Because you are correcting from 10 degrees in table A6 and from 20 degrees from table B2.
Table A6 is based on site testing conditions at an assumed conductor temperature of 10 degrees,where B2 is the resistance/meter or R1+R2/meter For cables at 20 degrees in milliohms per meter.
2 different temperatures will not give the same correction factor to be applied.
 
Because you are correcting from 10 degrees in table A6 and from 20 degrees from table B2.
Table A6 is based on site testing conditions at an assumed conductor temperature of 10 degrees,where B2 is the resistance/meter or R1+R2/meter For cables at 20 degrees in milliohms per meter.
2 different temperatures will not give the same correction factor to be applied.
thanks Ian,just trying to get my head round it,just don't get 2 values for same degree value
 
is it the case then its assumed b2 values are stated as that's what the expected temp when doing install
Yes when designing a circuit to determine a calculation of the R1+R2 for said circuit you would use the values given in b2 unless you need to temperature adjust and then multiply by 1.2 to convert to max operating temperature of 70 degrees assuming a max operating temperature of 70 degrees for cables used to connect to similar rated accessories and switchgear
 
The values in 7671 are not the corrected values for Zs.

Zs = ((Uo x Cmin)/Ia) x 0.8
Meaning ((230 x 0.95)/160) x 0.8 = 1.0925 which the book rounds up to 1.1 which is the value you'll find in the on-site guide and GN3.

The values in 7671 are at 100% whereas 80% is to allow for rises in temperature, with every 5 degrees you get 2% more resistance.

A6 corrects from 10° whereas B2 from 20° hence the 1.04 because that's the decimal percentage of 104%
 
The values in 7671 are not the corrected values for Zs.

Zs = ((Uo x Cmin)/Ia) x 0.8
Meaning ((230 x 0.95)/160) x 0.8 = 1.0925 which the book rounds up to 1.1 which is the value you'll find in the on-site guide and GN3.

The values in 7671 are at 100% whereas 80% is to allow for rises in temperature, with every 5 degrees you get 2% more resistance.

A6 corrects from 10° whereas B2 from 20° hence the 1.04 because that's the decimal percentage of 104%
thanks Christopher. but why are their two values 20c
 

Reply to guidance note 3,help please in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Replies
0
Views
273
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
818
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
534
Hi all, Just wondering if anyone can shed some light on the max zs values in the OSG, they don’t seem to follow the 1.25 divisor stated in the...
Replies
10
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock