Has anyone had this issue before ? Was working on a three phase board, when I took the cover off I noticed a black spot on one of the rcbo’s. it happened to be smouldering and started to catch a light. I noticed another rcbo smouldering too. I instantly turned off the main switch as one of the rcbo’s was tripped and still smoking. After investigation I found that the neutral tail had dropped out of its terminal. Is there a deeper problem here or should rcbo’s catch alight when dropping a neutral ?
 
Was that the Circuit Neutral dropping out of the RCBO or the Main Neutral dropping out of the Neutral bar?

What was the reason you went to the DB and needed to remove the cover.?
 
Was that the Circuit Neutral dropping out of the RCBO or the Main Neutral dropping out of the Neutral bar?

What was the reason you went to the DB and needed to remove the cover.?

The main neutral into the main switch.
Reason to be in the DB was installing new circuits.
 
Seems a bit fortunate.....installing new circuits and coming across such a serious problem!

Any evidence it's been ongoing?
 
Seems a bit fortunate.....installing new circuits and coming across such a serious problem!

Any evidence it's been ongoing?
It hasn’t been ongoing, was pulling in singles in trunking around the bottom of the DB must have pulled on the neutral tail. But that isn’t the issue. Regardless of how the neutral dropping out of the terminal, the rcbo’s shouldn’t combust when losing the neutral. If the electricity suppliers dropped a neutral off the pole would the house just go up in smoke because of it ?
 
Loss of neutral to a property is a very real and dangerous thing.
And yes, things can go up in smoke.

Highlights the importance of safe isolation and testing before re energising
 
It is quite possible that you have dameaged many single phase appliances
Without the N they can have 400v across them.
 
Loss of neutral to a property is a very real and dangerous thing.
And yes, things can go up in smoke.

Highlights the importance of safe isolation and testing before re energising
Safe isolation and testing wouldn’t work if the neutral fell from a power suppliers pole
 
Safe isolation and testing wouldn’t work if the neutral fell from a power suppliers pole
It happens quite often in rural locations, the local scrap metal thieves steal the N cable and the farm or farms end up with a fair amount of damaged equipment.

And in many situations, a loss of N would be picked up before re energising.
If I saw 3 to 4 hundred volts phase to N I would not be turning on the big red switch!
 
We weren’t re en
It happens quite often in rural locations, the local scrap metal thieves steal the N cable and the farm or farms end up with a fair amount of damaged equipment.

And in many situations, a loss of N would be picked up before re energising.
If I saw 3 to 4 hundred volts phase to N I would not be turning on the big red switch
It happens quite often in rural locations, the local scrap metal thieves steal the N cable and the farm or farms end up with a fair amount of damaged equipment.

And in many situations, a loss of N would be picked up before re energising.
If I saw 3 to 4 hundred volts phase to N I would not be turning on the big red switch!
This is in an islolated building, nothing was isolated as the only thing energised was led lighting which never failed. They stayed on so until finding the burning rcbo’s we never knew there was any fault.
 
There is another thread like this when testing and things went "bang".

Wonder if the FE arrangement is partly to blame, but that is not what I understood them to do and when I IR tested some by mistake they survived 500V DC (without smoke) showning only a few hundred kOhm (from memory).
 

Reply to Hagar rcbo’s in three phase board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Replies
9
Views
840
I’m currently doing some testing on some site temps I have a three phase trip system the tails from the head go into a 100 amp RCD which feeds a...
Replies
8
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi everyone, this ones a first for me but weve been asked install and use a three phase supply in a large new build house. The 16 way dis board is...
Replies
5
Views
2K
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
533

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock