Discuss Hair clippers refuse to run properly. in the Electrical Appliances Forum area at ElectriciansForums.net

Reaction score
2
I live off grid with only solar and generator power, I've been using hair clippers for years but now I have 3 sets of Wahl mains clippers none of which will run properly in any of my 3 inverters, nor a ( non inverter ) Honda generator. The motors / solonoids in the clippers run weakly and can't cut on the inverters, and haywire over powered off the geny, the adjustment screw on them does nothing. They are all 50 htz as are my power sources.

I adjusted the generator rpm right though its voltage range but nothing worked.



Before I junk all the clippers and buy rechargeable ones does anyone know what is going wrong ?
 
Hi -do you have any test gear? - what type of clippers are they (animal, hedge etc) ? Pic of the clipper and it's rating plate (if it's got one). What invertors do you have? :)
 
Thinking old school , go for genny .
Were clipppers only load on genny ?
If so -add an incandescent lightbulb / heater to
give it a 10 - 30% load . Or even try an old car battery charger + battery
to take some spikes off !
 
Inverters..

1. 56hz - 198 v
2. 67hz - 201 v
3. 51hz - 203 v

Generator at 230 v - 1540 - 1600 hz

That solves the mystery then ?

I knew the geny was out of spec, but not all three inverters.
 
I suspect the high speed switching on/off of the load is confusing the inverter and that the engine of the generator can’t keep up with the rapidly changing demand.

As suggested earlier a constant ballast load on the generator may help.
 
Don't you have a buddy or somewhere local with grid power where you can try them? It would be worth the effort to rule out the clippers themselves being the problem before trying to find a work around for a power problem that might not even be there....
 
Taking a guess,if they have oscillating coil mechanisms,and not conventional motors,it could be your waveform shape,which is upsetting them.
Something for the weekend,thought wise,anywho...
 
I'd guess the highly non-linear nature of the load (almost purely inductive) could be causing sufficient phase angle lagging to be having some strange effect on the output IGBT's of an inverter. Not sure what the generators excuse might be, possibly some similar effect on the output regulator, who knows.

I'd still rule out the clippers themselves being the problem first though.
 
Hi -do you have any test gear? - what type of clippers are they (animal, hedge etc) ? Pic of the clipper and it's rating plate (if it's got one). What invertors do you have? :)
the clue is in the thread title HAIR clippers
 

Reply to Hair clippers refuse to run properly. in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi, My Wahl Home Pro corded hair clipper has stopped working......3A fuse is still good. No sound, no movement , no nothing.......i took the blade...
Replies
2
Views
2K
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
Hi all, I've got a small catering business out of a converted horse trailer and purchased an inverter generator to power the trailer, mainly just...
Replies
8
Views
6K
I have a 115vac line that tests with proper voltage and will power a low watt bulb but will not run a drill etc... Line from main panel to barn...
Replies
3
Views
989
Hello, Apologies if these are really basic questions, I know next to nothing about electronics and such. I'm quite an outsider here. I'm looking...
Replies
2
Views
767

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock