Discuss Has this been done right? Im confused! in the DIY Electrical Advice area at ElectriciansForums.net

S

sjmleeds

Hi Guys,

I'm by no means an electrician but have never had any issues installing new ceiling lights, etc.

We've had an electrician re-wire the house and ive just come to fit the light fitting in one of the rooms, a ceiling rose. The light switch is like this, which has been wired as you can see, COM/L1, this done by the electrician.


IMG_0226.jpg



The ceiling rose only has 1 wire coming through as so, with a L/N/E, no matter how i connect these to the ceiling rose it just doesnt work. Can anyone shed any light on it for me please?

IMG_0230.jpg


IMG_0228.jpg


This is a box room with no other switches/lights, etc. Just 1 switch and 1 light.

Thanks in advance.
SJM
 
Did it work before you dismantled it?
 
looking at that rose, there's no connection between the browns. connect browns together. must be a JB above. and looks like old wiring ( double red) has been used for the switch wire.
 
The brown cable should be in the same terminal; block as the brown flex, it's been wired from a JB
 
Not a full rewire then?

No mate they wires are the right colour so it must be OK
You know Murdoch I wondered what you were getting at, they old age and dementia creeps up on you well I see now what you were getting at twin reds eh, dohh
 
Last edited:
deleted .
 
Hi Guys,

I'm by no means an electrician but have never had any issues installing new ceiling lights, etc.

We've had an electrician re-wire the house and ive just come to fit the light fitting in one of the rooms, a ceiling rose. The light switch is like this, which has been wired as you can see, COM/L1, this done by the electrician.


IMG_0226.jpg



The ceiling rose only has 1 wire coming through as so, with a L/N/E, no matter how i connect these to the ceiling rose it just doesnt work. Can anyone shed any light on it for me please?

IMG_0230.jpg


IMG_0228.jpg


This is a box room with no other switches/lights, etc. Just 1 switch and 1 light.

Thanks in advance.
SJM

I hope you didn't pay for a complete rewire as you've been done.

What did the cert say?
 

Reply to Has this been done right? Im confused! in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
453
Hi, I need some advice on the wiring for a new ceiling light. I have taken down the original light, and I'm left with the wiring in the image...
Replies
6
Views
1K
Hello, Looking for DIY electrical advice. I have 7 x spots, and each are fitted with 1 x T&E connector block fitting [see photo]. In the past...
Replies
3
Views
653
L
WIRING FOR WALL SMART SWITCH FOR CEILING FAN/LIGHT Just bought a smart wall switch for a ceiling fan/light currently connected to a single switch...
Replies
0
Views
719
littletwinn
L
Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Replies
23
Views
703

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock