Discuss heating controls in the Central Heating Systems area at ElectriciansForums.net

G

garymul

Hi folks looking for a bit of advice, my boiler fires up when there is no call for heating or hot water, the motorised valves for the heating and hot water are both closed but boiler still comes on, i thought that when the motorised valves are shut this cuts off the suply to the boiler and pump. The pump seems to always be running, dont think the motorised valves are faulty due to them only being 2 years old, is there a possible fault in the wiring ? Any advice would be appreciated, thanks
 
Depending on the type of boiler you may have a small hot water storage tank that is being kept hot to ensure instant hot water, this option is normally able to be switched off in the programming.

Alternatively if you have a frost stat on the circuit and this is set too high then the boiler may come on when the frost stat thinks it is too cold.
 
Hi folks looking for a bit of advice, my boiler fires up when there is no call for heating or hot water, the motorised valves for the heating and hot water are both closed but boiler still comes on, i thought that when the motorised valves are shut this cuts off the suply to the boiler and pump. The pump seems to always be running, dont think the motorised valves are faulty due to them only being 2 years old, is there a possible fault in the wiring ? Any advice would be appreciated, thanks

It could be a number of things so without testing it's just guessing. It could be as Richard described or a micro switch could be sticking between the grey and orange on one of the valves or could be an internal fault on the boiler. Get an electrician to check the correct voltage is present at each sequence of switching between programmer, thermostats, valves and boiler.
 
Faulty valve switch, or faulty programmer relay.
You need to disassemble the wiring at the junction box, and test it live to see where the fault is - dont do this if you are not experienced.
 
Found the problem, the orange wire from the heating MV is constantly live even tho the valve is switched off and there is no supply from the brown wire, the actuator is only 1 year old which is why i found it strange for it to be faulty, surely they should have a warrenty or something if the valve goes faulty only after a year, cheers for the advice
 
Found the problem, the orange wire from the heating MV is constantly live even tho the valve is switched off and there is no supply from the brown wire, the actuator is only 1 year old which is why i found it strange for it to be faulty, surely they should have a warrenty or something if the valve goes faulty only after a year, cheers for the advice

Is the valve spring returning when the supply is turned off? If it is the micro switch is up the swanny, if it isn't returning the body of the valve could be seized and holding the micro switched closed.
 
The valve body is opening and closine fine, the fact that when i turn the htg stat down and it cuts off the supply to the brown wire could only really indicate a internal fault in the actuator since the grey live wire must somehow be connrcted to the orange, cant see it being a wiring fault
 
The valve body is opening and closine fine, the fact that when i turn the htg stat down and it cuts off the supply to the brown wire could only really indicate a internal fault in the actuator since the grey live wire must somehow be connrcted to the orange, cant see it being a wiring fault


When 230V is supplied to the brown synchron motor connection the motor begins to turn. The motor is mechanically linked to the valve spindle which opens the valve as the motor turns. Also mechanically linked to the motor is a small arm that acts upon the micro switch when the valve has fully opened. When the valve is in the open position the synchron motor stalls.Since it's not a good idea to simply demand heat while the valve is being supplied 230V to the brown motor connection, the micro switch comes in to play. As the micro switch has now changed state due to the valves internal arm acting on it there is now continuity between the orange and grey wires that are directly connected to the switch. At rest there is no continuity between these wires. It is the micro switch that gives the demand for heat, and letting the boiler know it's ok to fire up.When the 230V supply is interrupted to the brown motor connection, the motor comes out of it's stalled state and the valve is pulled closed by an internal spring. As this happens the internal arm lifts off the micro switch changing its state back to open circuit between orange and grey.
 

Attachments

  • image.jpg
    14.3 KB · Views: 62
Occasionally I've found that if the 'arm' is very slightly bent [mainly on Danfoss valves] it can slip into the notch at the end of it's travel which is there for manual override/ testing purposes, if it does it will stay there indefinitely until manually released and the boiler/pump will continue getting a switched live supply regardless of control and thermostat settings, this is rare but worth checking anyway.
 

Reply to heating controls in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
951
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
663
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
619
Hi everyone, my house has an air-to-heat system that generates hot water in a boiler. This boiler is then connected to the central heating...
Replies
1
Views
814
1 - Major supply fault, details unknown. By time I get there DNO already put in genny and are digging up road. 2 - Reason for call, heating not...
Replies
4
Views
601

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock