This problem solving was on Virtual Scenarios (Ring Final Circuit) Getting Value of R1+R2

2.5mm and 1.5mm size cable used.

1st From the C.U. values of following connection
L to L =0.27
N to N =0.27
CPC to CPC =0.45

2nd from the C.U cross the outgoing L to the incoming N and vice versa
Measure between L and N at each socket outlet.

socket 1 = 0.16
socket 2 = 0.16
socket 3 = 0.17
socket 4 = 0.18
socket 5 = 0.46

3rd from the C.U cross the outgoing L to the incoming CPC and vice versa
Measure between L and CPC at each socket outlet.

socket 1 = 0.73
socket 2 = 0.73
socket 3 = 0.75
socket 4 = 0.74
socket 5 = 1.2

I'm confused which of the value of R1+R2 to be recorded?
Is there something to be calculated to get the value of R1+R2?
 
With those readings I would say that socket 5 is a spur - so take it off the wall and check it has only 1 cable - if it has 2 cables it may still be a spur with a spur off a spur OR be a dodgy socket, so try the readings off the cables.

hope this helps

Ps you record the highest reading
 
Last edited by a moderator:
Have another look at your Line and CPC results you should be getting around 0.18 at each of the points and as Murdoch has said find out why you are getting the high reading at the last S/O !!
 
2.5mm+1.5mm T&E. r1 and rn should have the same value of resistance measured end to end (within 0.05 of each other). r2 is obviously going to be of a higher value of resistance than r1 or rn due to the CPC being of a smaller CSA (times the value of r1 by 1.67). The value of r1 and the value r2 added together and then divided by four will give you your R1+R2 value.
 

Reply to Help me to Understand to get value of R1+R2 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original...
Replies
6
Views
2K
No photo's as customer is already in dispute with kitchen fitter and was very strict about it! I went to look at what would be involved to add a...
Replies
3
Views
1K
Hi All, Busy doing an EICR and on 2 of the Socket Rings for the dead test I get the following results: Step 1: End to End (0.32 ohm r1, N ) & (r2...
Replies
9
Views
4K
Hi guys, I just need help with something really basic that I’m struggling with in terms of calculating resistance (as opposed to measuring)...
Replies
11
Views
12K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock