Discuss Help Picking A Generator in the Australia area at ElectriciansForums.net

P

ptotten@hotmail

Hi there, I was wondering if anyone can help me out at all as I have tried all my local contacts and services and have had no luck at all.
Basically I own a car repair garage and have purchased a 3 phase rolling brake tester unit which has 2 x 3.7 kw motors in it as well as a control panel, the only problem is that in my workshop is only single phase electric which is piggy bacedk from a joining house.
I dont really fancy the idea of running a power convertor as i do not think that the supply coming into the workshop is heavy enough.
I hired out a 20kva 3 phase generator and it powered the brake tester with no problems so I know this is enough but I was wondering if a less kva powered unit would do, as in a 10kva as they seem cheaper and easier to get aswell as smaller. i have tried to hire a 10kva unit but no one in my area in northern ireland seems to hire one as they are supposidly not commonly asked for.
Any help or any ways to work this out would be GREATLY appriciated.
 
Yea I know what you mean but 2 problems,
1- I dont have 3 grand to spare at the minute
2- I'm not sure how long i am staying in my current location, where as I can take a generator with me anywhere I go
 
were abouts in northern ireland are ye? try these guys trooperslane carrickfergus
Email: [email protected] Tel: +44 (28) 9336 4779 or alternativately if ye want to buy new
FG Wilson Ltd
Old Glenarm Road
Larne
Co. Antrim
N. Ireland
BT40 1EJ
Tel. +44 (0) 28 2826 1000
Fax. +44 (0) 28 2826 1111
hope this helps
 

Reply to Help Picking A Generator in the Australia area at ElectriciansForums.net

Similar Threads

Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
658
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
710
Hi there, I’ve hired a marquee for an event next month but am a bit lost on how to power it. There are 2 sockets 50 metres from the marquee and 2...
Replies
1
Views
2K
Iv been asked to wire a separator (portable to go to different farms and separate water from slurry) to a 3phase 40 kva generator. The separator...
Replies
4
Views
2K
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock