Discuss Help with a tripping washing machine in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Hi Guys,
I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used.
The fuse board is an MEM Memera 2000
the downstairs ring is on a 32A 60898 MCB, protected by a 61008 RCD 100A 30mA
there are 2 other circuits on the same RCD which are the upstairs rings on a 32A 60898, and the shower also on a 32A 60898

The customer had this problem before I came and had already tried replacing the washing machine and getting the same problem.
  • we have carried out fault finding and also EICR'd the whole house with perfect results,
  • we have tried plugging in the washing machine upstairs which is the same RCD and it didn't trip. and also on another circuit in the garage on a different RCD which also didn't trip (both times the washing machine stayed in the same position in the kitchen under the worktop and was just plugged into different sockets via an extension lead
  • we have also tightened all connections on the downstairs ring assuming that maybe the washing machine vibrating could have caused a loose connection and tried fault finding again and cant find any problems
  • we have also tested for overload by unplugging every other thing on the circuit and it still trips
  • we have also replaced both the RCD and the MCB and still it keeps tripping
  • I have tried plugging into other sockets on the same circuit and it still trips
  • I have also tried replacing the socket its plugged into just in case

Yet we cant find any fault so I'm absolutely stumped, is there anything I've forgotten to do?

Thank you in advance, I'm loosing hair over this problem haha

Test results for Downstairs socket ring
R1 0.57
RN 0.57
R2 0.95
R1+R2 0.38
Zs 0.63
RCD 1/2x didn't trip
RCD 1x 27.8ms
 
At what point of the WM cycle does it trip? Immediately or after a while?

Was the replacement RCD exactly the same one, or was another type substituted?
Yes it was, I did however make a mistake the RCD’s are
At what point of the WM cycle does it trip? Immediately or after a while?

Was the replacement RCD exactly the same one, or was another type substituted?
The customer told me it trips virtually straight away as soon as the cycle starts,
I went to the property yesterday and it wouldn’t trip for me, however now that I’m thinking about it it was empty and not a full washing load when I tested it for overload,

Also the RCD was the same yes, although if it helps I did make a mistake it’s a BS 4293 type 2, not 61008 weather that makes a difference or not
 
Sounds like the fault is intermittent, which means some of the things that have been tried may have given misleading results. Also sounds like it's unlikely to be a circuit fault, which points to either the RCD or WM (my money's on the latter).

Have you IR tested the WM itself? Good to do this immediately after the tripping event too, if possible. I would try leaving it plugged into one of the other circuits via extension lead for a week or 2, and see if it trips the RCD then.
 
Recently traced a similar fault to an isolator switch. Everything pointed towards a faulty appliance, but it was fairly new and an expensive machine and I wanted to return to clamp it and check for leakage throughout the cycle. The switch didn't feel quite right (nothing obvious, but wasn't happy with its operation) and I decided to change it while there, for the sake of a few pounds. Previously the appliance had tripped about once in every three cycles and since hasn't tripped once in the last few weeks - maybe it'll act up again, but it appears as though I found the fault by accident and through sheer blind luck.
 
Sounds like the fault is intermittent, which means some of the things that have been tried may have given misleading results. Also sounds like it's unlikely to be a circuit fault, which points to either the RCD or WM (my money's on the latter).

Have you IR tested the WM itself? Good to do this immediately after the tripping event too, if possible. I would try leaving it plugged into one of the other circuits via extension lead for a week or 2, and see if it trips the RCD then.
the customer has said she has tried it multiple times in a upstairs socket on the same RCD via extension lead and in a socket in the garage on another RCD and it didn’t trip,

But yes I will try IR the machine itself, it just seems very strange that it could possibly be a another faulty washing machine as she replaced it already due to this problem, and the last thing I want to do is sent her down the path of trying to have it replaced again and it still causes a problem,

Thank you very much for your help tho, I must admit it seems to me unless it is the washing machine again it has to be an intermittent fault, possibly due to the vibration while it has a full load, I just have no idea how to solve it as it I’ve already tightened all connections in every socket/spur in the kitchen

Other wise perhaps I’ll wire a dedicated supply for it

I also got her to try the kettle in the same socket today and that didn’t trip it 😭

So I’m totally stumped haha
Many thanks for your help, I’ll go and try what you’ve said on Monday

Cheers
Chris
 
Recently traced a similar fault to an isolator switch. Everything pointed towards a faulty appliance, but it was fairly new and an expensive machine and I wanted to return to clamp it and check for leakage throughout the cycle. The switch didn't feel quite right (nothing obvious, but wasn't happy with its operation) and I decided to change it while there, for the sake of a few pounds. Previously the appliance had tripped about once in every three cycles and since hasn't tripped once in the last few weeks - maybe it'll act up again, but it appears as though I found the fault by accident and through sheer blind luck.
Yes, I think I’ll also do that, perhaps although the connections are tight it could be a faulty fused spur and the problem only occurs when it’s heavily vibrating with a full loads,
Thanks for your help
 
Yes, I think I’ll also do that, perhaps although the connections are tight it could be a faulty fused spur and the problem only occurs when it’s heavily vibrating with a full loads,
Thanks for your help

It's a long shot and the switch I replaced appeared fine visually, with all terminations sound and each conductor clean and bright. Now that I remember it was also a switched fused spur and in as new condition, other than some slight feel to the switch operation that wasn't quite right.
 

Reply to Help with a tripping washing machine in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hj our washing machine tripped out electrics the other day. Everytime we switched it in the electrics cut out. We noticed a larger bend in the...
Replies
0
Views
460
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
612
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
755
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock