Discuss Help with dimmable LED panel lights in the Commercial Electrical Advice area at ElectriciansForums.net

E

EndlessHysteria

Hi all,
To be clear I am still new to the job and this is the first time I've dealt with this situation.

I'm installing LED panel lights in a suspended ceiling, I've used dimmable drivers connected to the switched live and neutral on the input. And live and neutral on the output.

I've replaced the existing switches with rocker switch dimmers connected to permanent live and switched live.

Problem I'm having is that when the switch is pressed the light activates, however when the switch is releases and rocks back the light turns off.

Please any advice would be welcome as I've not dealt with dimmable LED panel lights before and I know I've still got a lot to learn in the trade
 
You have to put in a control cable and get a rotary analogue switch 0-10v. You put these on the + - outputs on your driver. Can you post a pic? So you have one switch for mains and one for the dimming usually grid switches.
 
EndlessHysteria can you confirm the 'rocker switch dimmers' manufacturer and part number. If you are referring to a 3way retractive switch then these alone will not tell a dimmable driver to 'dim'.

Sounds like you will need a edge dimmer to replace the switches you already have. The drivers will dictate whether you need leading or trailing type dimmers. What do the manufactures instructions say regards the LED drivers?
 

Reply to Help with dimmable LED panel lights in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I have a led panel that i want to dim. It is dimmable but without a dimmable driver. I have a dimmer module and a dimmer switch as shown in the...
Replies
0
Views
541
Hi all I've been changing the halogen downlighters in my house to LED's. I have three rooms that use dimmers, two of them have two switches each...
Replies
0
Views
370
I have purchased spotlights as below, but they are flickering when I dimmed them down to around 15-20%. We have installed 8 x ALUSSO LED Recessed...
Replies
4
Views
1K
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
691
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
446

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock