Discuss Help with Readings on circuit in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
1
Hi
Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main wired in 2.5mm twin on B32 Rcbo. There are 8 sockets on the ring and all are in plastic dado trunking in 2 offices. The readings I have are:
L-L= 0.76
N-N= 0.76
E-E= 1.32
R1/R2= 0.89
Zs= 0.78

Board ZS= 0.22

My R1/R2 are slightly high as should be roughly 0.52 so could that be trapped insulation in terminal instead of touching copper?

Also my zs was low at 0.78 when should be around 1.11. It can’t be parallel earth paths as everything is in plastic dado trunking.

Any help would be much appreciated in helping me further with my testing which needs brushing up more on.

Thanks
 
The L/N figures are consistent with the E so it looks to be fine. However, that seems consistent with 100m or so of cable so presumably a big area?

How did you measure the R1+R2 (I'm guessing a typo for "R1/R2" ?) as you say (r1+r2)/4 = 0.52 ohms? Did you null out any 13A plug to 4mm adaptor lead before checking?

Zs is in keeping with Zdb + computed R1+R2 but then many MFT assume a test lead (at least that is what DiLOG told me about lead nulling).
 
Ring final testing for R1+R2 is imperfect, and the results can be misleading.

For a ring final figure-of-8 test, results = (r1+r2)/4 only when measured at points on the ring. All spurs will give a higher result, no matter where they are on the ring. For example:

A very short spur taken from a point very close to the circuit origin would create a very short fault loop, this is obvious. However, when tested 'by the book', it would have a higher R1+R2 than a point actually on the ring, midway round the ring.

In your case, I expect you have tested correctly 'by the book'. The R1+R2 was probably taken at a spur, and the Zs measured at that spur more accurately represents the true fault path at that point.
 
Hi. I thought that it maybe a spur but I’ve checked all points on circuit and definitely no spurs on the ring.
I know expected readings never regularly match up but most are there or thereabouts. Which is why I was hoping someone maybe able to shed some light on it.
Appreciate your feedback!
 
Hi everyone. There is no boiler etc or spur on circuit I can confirm. When testing I did use the plug top attachment lead. I added 4 new Mk twin sockets to the ring and the reading on these were near enough the same as old ones in adjacent office.
I must also admit that I hate the megger tester I’ve been given from work. It has the confidence meter to it so takes ages to get a ZS reading due to harmonics on circuit. Give me a fluke any day of the week. The megger can take up to 2 mins per zs test.

Thanks
 

Reply to Help with Readings on circuit in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
509
Hi Help please with the adiabatic I am doing a small design for my course and I can't figure it out. Any advice will be appreciated. Ring Final...
Replies
15
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock