Discuss Help with wiring a shower switch in the DIY Electrical Advice area at ElectriciansForums.net

P

Paul197883

Hello there,

I need to sense check a shower switch wiring diagram. I've removed the old shower switch (broken cord) and have a new one ready to go. I'm sure it's a generic stamp on the switch but the old one says 'MAINS' inbetween the L and the N. The new one says 'AC only' between two neutrals.

I'm pretty sure these are not specific to the wiring and just stamps on the switch but can someone check my attached photos and confirm everything is okay?

Also, does it matter which earth wire goes in which earth socket as the bracket holding them in the new switch is at right angles ?
img1.png img1.JPG
 
Last edited by a moderator:
That’ll be ok. Earth can go in any of the earth terminals.
One thing, is it the photo, or are the black/red conductors smaller than the brown/blue ones?
 
Hello there,

I need to sense check a shower switch wiring diagram. I've removed the old shower switch (broken cord) and have a new one ready to go. I'm sure it's a generic stamp on the switch but the old one says 'MAINS' inbetween the L and the N. The new one says 'AC only' between two neutrals.

I'm pretty sure these are not specific to the wiring and just stamps on the switch but can someone check my attached photos and confirm everything is okay?

Also, does it matter which earth wire goes in which earth socket as the bracket holding them in the new switch is at right angles ?
View attachment 40224 View attachment 40225
If it was just the cord broken, why bother to change the complete switch, there doesn't appear to be a neon indicator on the replacement.
The Bathroom or shower room constitute a "special location" the Shower is a high current user and thus will require an experienced person to change the switch to ensure good tight connections, lost count of the number of burnt out switches due to poor installation, I would say an MNW certificate will be required, some may dispute that statement, if it is installed by yourself as a lay person, and it causes a fire your insurance may be compromised, get an Electrician in to replace the switch for you, peace of mind is a wonderful thing. Sorry for the ramble, but would hate to see you struggle.
 
Yes, the brown and blue wires are thicker than the black/red.
The latter look like standard wiring to me and the brown/blue are quite chunky wires. I was surprised how thick these were.
w2.jpg
 
If it was just the cord broken, why bother to change the complete switch, there doesn't appear to be a neon indicator on the replacement.
The Bathroom or shower room constitute a "special location" the Shower is a high current user and thus will require an experienced person to change the switch to ensure good tight connections, lost count of the number of burnt out switches due to poor installation, I would say an MNW certificate will be required, some may dispute that statement, if it is installed by yourself as a lay person, and it causes a fire your insurance may be compromised, get an Electrician in to replace the switch for you, peace of mind is a wonderful thing. Sorry for the ramble, but would hate to see you struggle.
 
Fair comment. I've been quote £80+vat. There is a neon switch on the replacement.
 
looks to me likeit's a 6.0mm circuit and someone has replaced the cable to the shower with 10.0mm( possibly on a shower upgrade). what's the rating of the MCB supplying the shower circuit.

also, i's be inclined to swap that new switch for a crabtree one. much easier to get 10mm in.
 
looks to me likeit's a 6.0mm circuit and someone has replaced the cable to the shower with 10.0mm( possibly on a shower upgrade). what's the rating of the MCB supplying the shower circuit.

also, i's be inclined to swap that new switch for a crabtree one. much easier to get 10mm in.

looks like earth is single strand on red and black cable so probably at most 6mm the other earth is multi strand so possibly 10mm as you said .
some plier marks on the insulation of cables as well ..night be worth an electrician checking the job to check the route is ok for 6mm then 10mm cable..against the shower rating voltage drop etc
and testing the cable prior to switch on in case of insulation damage
 
i'd charge £80 but that would include a crabby 50A switch/isolator. fed up of pi$$ing about with other types.only ever once had a crabby fail and that had been in 25 years. i know as i installed it in 1985
 
it would if i did it. and i'd check tightness of connections in CU. no wonder i'm skint. too soft 4 my own good.
hahaha I'm the same. I think, I'm too cheap as well and that's why I'm skint also...
just been on a job and plumber was charging nearly double what I was and he was there half the time ...
 

Reply to Help with wiring a shower switch in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I have a 220v House I want to change this switch to smart switch, but I am stumped, I don't have a neutral so I had to return the switch I...
Replies
2
Views
700
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
992
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
491
Hi, The shower pull chord switch has snapped at my mom’s home and having unscrewed the switch I discovered a horror show(see pic). So I’ve had...
Replies
39
Views
3K
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
331

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock