Hi all

I am fitting a new Crabtree High Integrity CU tomorrow at customers premises, as it is all solid floors DS & chipboard US with glued downcarpets. I am proposing to use the redundant cooker cable (gas cooker now fitted) as a feed sub main circuit to supply the integral garage via 32A CB.

I was thinking of using a 3 way garage CU in the garage to feed the garage elecs and use the 3rd way to provide a feed to a WP JB and SWA to the shed.

How do I provide discrimination as all three CU's have 30ma RCD's the HI CU does not have any non RCD spare ways and in any case as I am using the existing cooker circuit which is buried in the wall I will need RCD protection for that part of the sub main.

Any suggestions on the discrimination side or is there a better way of doing things without taking half the house to pieces?

Cheers

Mark
 
As Jason said, or use an rcbo in one of the unprotected ways of your high integ board. Bit more expensive though (Around £25-00 for the rcbo) :)
 
are you saying that the rcd in db1 will protect the submain to db2 and db3 hence you can put db2 and db3 circuits on non rcd boards just asking as i had this problem and that is what i did as i could not acheive discrimination and the most sensitive rcd in db1 was allways knocked out 1st even if the fault was in bd3 !!
thanks
Rich:)
 
If your submain is protected by an rcd from main board ie DB1 then the board that submain supplys will only need a mainswitch and mcb combination. A new high integ board has dual RCDs so one submain could be fed from the first rcd with the second submain from the 2nd rcd. Alternatively, seeing as its a high integ board you could use an rcbo which would give the submains dedicated protection, but at extra cost.;)
 

Reply to Hi Integrity CU in the Australia area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
978
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
913
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
904
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
320
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock