Discuss High continuity resistance on ring final circuit in the UK Electrical Forum area at ElectriciansForums.net

kkkkk

-
Reaction score
18
Hi peeps

I have continuity measurements on a ring final circuit of: L/L 1.4, N/N 0.78, E/E 1.7
Loose connections somewhere?
There is a new CU with RCD.
Insulation resistance measurements are good.
There is a boiler added into the circuit as a spur.
Any suggestions or comments?

THANKS!!
:) :) :)
 
Well, first glance says that you're using 6242Y, therefore the cpc is going to be roughly .7 again your main conductor, therefore your N & CPC values are [high-ish] but vaguely in keeping with this ratio, therefore you have an issue with your live conductor somewhere.
 
Check connections/terminations for something corroded, loose or even overtightened. Maybe check where the spur is for a wire that got a haircut.
 
A "ring" within a "ring" can cause them sort of readings on a circuit wired in single sometimes, also could be done with twin, but a lot more difficult to do with t&e
 
0.6 Ohm is not that bad, its hard to get it exactly right especially when many points on the ring, if you have bit of time get a wander lead and wander around doing continuity testing. e-e supposed to be higher anyway because of smaller wire csa.
 
0.6 Ohm is not that bad, its hard to get it exactly right especially when many points on the ring, if you have bit of time get a wander lead and wander around doing continuity testing. e-e supposed to be higher anyway because of smaller wire csa.


But what about the L/L value being nearly the same value as the CPC
 
0.6 Ohm is not that bad, its hard to get it exactly right especially when many points on the ring, if you have bit of time get a wander lead and wander around doing continuity testing. e-e supposed to be higher anyway because of smaller wire csa.

Sorry mate but I have to disagree. 0.60 ohms difference between 2 identical core sizes on a circuit is NOT good. Typical tolerance is + or - 0.05 ohms.

Looks like the issue should be investigated.
 
it only needs 1 poor connection at a socket to give this sort of anomaly. nothing for it but to go round every accessory till you find it.
 
it only needs 1 poor connection at a socket to give this sort of anomaly. nothing for it but to go round every accessory till you find it.
well ...its a ring final isn`t it...

so alls he has to do is get the wander lead out.....pick a leg at the board....

then go round with the breakout box....till he gets to the outlet where the value jumps up abnormally....

its either the outlet he`s testing....or the one prior to that one...
 
problem with that,glenn, is that he's then reading through the socket and it's switch. better to go in at the back, as the actress said to the bishop.
 
glenn can you get that CM400 at the right price, mate?
 

Reply to High continuity resistance on ring final circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock