Have been roped into assisting with a 100 metre SWA run at appr. 4.0-6.0m high, the guy has not priced to fit strut or tray and intends to cleat to wall and cable-tie to existing larger armoureds, trouble is I know how this guy works....on a 'shoe-string'!!
Any suggestions on best/easiest way of 4 blokes managing this SWA, bear in mind its in hospital grounds and under a 'watchful-eye' of health and safety etc!!!
Has been mentioned about using a scissor lift/cherry-picker that's on site already but I know that's just not enough and 4 blokes isn't enough.
 
Sounds like a recipe for disaster with what this bloke is planning.

I have used a scissor lifter to lift large SWA up to brackets before and its not too bad. But we had about 6 blokes, the scissor lifter, nice big cable jacks, and plenty of cable rollers. We were using purpose made unistrut brackets to support these cables and wouldn't have entertained just using cleats for a cable that size at that height.

A cherry picker won't take any sort of weight at all so don't even think about using one of those.
 
100Mts 95mm SWA is that three or four core, I'd cut it into 10 Mt lengths then four men could handle it easily, you'd have a few terminations to do but shared between 4 men shouldn't be too hard, you may have to all balance on each others shoulders to reach to do the glanding but I think I know the chap who's priced the work is his name "Billy Smart" this should be some performance lol
 
to cleat to wall and cable-tie to existing larger armoureds, trouble is I know how this guy works....on a 'shoe-string'!!
Any suggestions on best/easiest way of 4 blokes managing this SWA, bear in mind its in hospital grounds and under a 'watchful-eye' of health and safety etc!!!

And that installation is acceptable to the Hospital Engineer is it??

Number One, you don't cable tie to existing installed cables, all your doing is adding additional weight to the fixings of that cable, maybe beyond it's capabilities!! Also, most cable ties are not designed to carry weight, but only to hold cables in place, ...such as on a cable tray/basket.


It's hard enough installing 100m of 95mm SWA cables on cable tray at that height, cleating it at that height, with that number of manpower, and without the correct equipment and your all just asking for an accident to happen!!

Pretty sure the H&S officer will put a stop to this little adventure as soon as he sees what's going on!! ...lol!!
 
Pulling in 100m of 95mm 4c would be hard enough through ducts, never mind at height. I take it that you've not ever been back to older installations, where heavy cables are supported by cable ties.
They age, weaken and snap.
There is a paper mill not far from me, where this has become a big problem.
as mentioned, you need decent containment, rollers, lifting gear and decent labour.
 
Sound like a nightmare you need skill to even pull in an armoured and get twists in the right places for bends and that 4 men could be enough with good planning and the right floor space but the fixings sound like a death trap
 
I dont really see a big issue with only 4 men, of course it would be easier with more but 4's not a problem.

Only having a scissor lift is though and the way its being installed, 95mm SWA cable tied to existing cables!?.

Who's the guy whos priced it up then? an electrician? get him told its wrong. In a hospital grounds too, wouldnt of though this would be allowed...
 
I dont really see a big issue with only 4 men, of course it would be easier with more but 4's not a problem.

Only having a scissor lift is though and the way its being installed, 95mm SWA cable tied to existing cables!?.

Who's the guy whos priced it up then? an electrician? get him told its wrong. In a hospital grounds too, wouldnt of though this would be allowed...

depends on the hospital, one my company has been working in for years is very strict.

if the guy doesnt get it his way its goodby and he wont allow your company back for as long as he is working there
 
depends on the hospital, one my company has been working in for years is very strict.

if the guy doesnt get it his way its goodby and he wont allow your company back for as long as he is working there

And exactly as it should be!! He at the end of the day, is responsible for the smooth running of all the services on the engineering side of that hospital!!
 
What is he fixing the cleats with? Rawl bolts? Or inch and a half 8's haha.

If if you haven't got a cable jack, if there's enough space, run the cable in an S on the floor, your only dragging a section of the cable then, Not the whole 100m.

I wouldn't want to be near if you drop that cable from 6m either!!
 
Get one of you to book in at Casuality before you start that way when one or all of you injure yourself it will avoid waiting in the 3hr queue !!
Seriously walk away or ask to see hi RA & MS as Hospital will require this as standard.
 
Number One, you don't cable tie to existing installed cables, all your doing is adding additional weight to the fixings of that cable, maybe beyond it's capabilities!! Also, most cable ties are not designed to carry weight, but only to hold cables in place, ...such as on a cable tray/basket.QUOTE]

But you haven't mentioned 'grouping factors' mate :30:
 
It's hard enough installing 100m of 95mm SWA cables on cable tray at that height, cleating it at that height, with that number of manpower, and without the correct equipment and your all just asking for an accident to happen!!
But on the plus side, they are already on site at the hospital so A&E shouldn't be far away :)
 
I,ve contracted in a hospital and it,s hard enough to get a parking permit,there is absolutely no way that their engineer is going to have this.even if you manage to lash it in without him seeing it I can guarantee he'll tell you to rip it out and do it properly,that,s assuming he doesn't specify how he wants it done in the first place.
 
Have been roped into assisting with a 100 metre SWA run at appr. 4.0-6.0m high, the guy has not priced to fit strut or tray and intends to cleat to wall and cable-tie to existing larger armoureds, trouble is I know how this guy works....on a 'shoe-string'!!
Any suggestions on best/easiest way of 4 blokes managing this SWA, bear in mind its in hospital grounds and under a 'watchful-eye' of health and safety etc!!!
Has been mentioned about using a scissor lift/cherry-picker that's on site already but I know that's just not enough and 4 blokes isn't enough.

This contractor reminds me of someone on t.v.........



Cletus.gif

;-D
 
My old man is the main Electrical on-site chief whip engineer for a local hospital and they are very strict and ensure all design and installs meet strict requirements.... i don't get the OP post, he's posted it asked for suggestions and disappeared if this set-up is as he suggests then as soon as their own in-house Engineers see the work they will ask for it re-doing, they should have been given a design draft or asked to submit one for confirmation...... something just dosn't ring true here!!
 
not the engineerinh head the actual head of the hospital, he keeps a very active role


If he has any sense, he'll be taking guidance from the Hospital Engineer, as this is the guy that has the overall responsibility for all the engineering services within the hospital, not the Hospital Administrator or whatever they call them these days!! May be your guy has made the jump from being a Hospital Engineer to Administrator, and so would know what he's talking about, or perhaps this is a small hospital and is in a dual role as Hospital Engineer and Administrator...

From my experience, and i've spent a good many years of my career in Hospital construction projects and maintenance, the Hospital Engineers i have known, and interviewed are no-bodies dummies, they can't afford to be!!
 
If he has any sense, he'll be taking guidance from the Hospital Engineer, as this is the guy that has the overall responsibility for all the engineering services within the hospital, not the Hospital Administrator or whatever they call them these days!! May be your guy has made the jump from being a Hospital Engineer to Administrator, and so would know what he's talking about, or perhaps this is a small hospital and is in a dual role as Hospital Engineer and Administrator...

From my experience, and i've spent a good many years of my career in Hospital construction projects and maintenance, the Hospital Engineers i have known, and interviewed are no-bodies dummies, they can't afford to be!!

he made the leap and knows the place better than any current employee.
 
100Mts 95mm SWA is that three or four core, I'd cut it into 10 Mt lengths then four men could handle it easily, you'd have a few terminations to do but shared between 4 men shouldn't be too hard, you may have to all balance on each others shoulders to reach to do the glanding but I think I know the chap who's priced the work is his name "Billy Smart" this should be some performance lol
great idea mate then with the short lenghts to the nearest scrap yard thats great bloke to work for did his big stetson on his head not give him away
 
Did a job like this in Leeds, 1998. Bank call centre basement. There were about 15 of us, loads of rope and two forklifts. This size SWA categorically goes on its own heavy duty tray.
 
a dont get the guys on here "walk away" "walk away" why? because its a tough job and the cable size is over 2.5 get stuck in , tell the guy ur not happy and its better to cleat it the whole run as said in above posts cable jacks and rollers scissor lift and 4 men, job done aye its a nightmare but the hard jobs are what make you a better spark .
 
a dont get the guys on here "walk away" "walk away" why? because its a tough job and the cable size is over 2.5 get stuck in , tell the guy ur not happy and its better to cleat it the whole run as said in above posts cable jacks and rollers scissor lift and 4 men, job done aye its a nightmare but the hard jobs are what make you a better spark .



4 guy's working in/under unsafe conditions installing what is going to be a total lash-up, will not under any stretch of the imagination, make you a better spark!!
 
a dont get the guys on here "walk away" "walk away" why? because its a tough job and the cable size is over 2.5 get stuck in , tell the guy ur not happy and its better to cleat it the whole run as said in above posts cable jacks and rollers scissor lift and 4 men, job done aye its a nightmare but the hard jobs are what make you a better spark .

Get real! Four crippled or dead sparks is more like.
 
Think about the logistics for a second.
You need one man on the drum, to stop it coming off the jacks.
one man to guide it on the tray, and to pull it from the jacks.
At least one man per bend, and one every 10-20 m at least. Just lifting the cable up to the tray will be hard enough. Get the boss some gloves, and boots, and get him to help. He won't ask the same of you again!
 
Think about the logistics for a second.
You need one man on the drum, to stop it coming off the jacks.
one man to guide it on the tray, and to pull it from the jacks.
At least one man per bend, and one every 10-20 m at least. Just lifting the cable up to the tray will be hard enough. Get the boss some gloves, and boots, and get him to help. He won't ask the same of you again!

What cable tray?? The idea here is to cleat and cable tie onto existing cables!! lol!!
 

Reply to high level 95mm2 SWA run in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Just installed a 70 mm 4 core Swa,height 5m on existing ladder rack. 120m,straight run with 90° turn. Struggled with what we had but it’s in...
Replies
4
Views
923
Was asked to quote for a job today wiring up a summerhouse/playhouse in a garden to run the usual sockets, lights and garden tools etc... When on...
Replies
13
Views
3K
J
View From The Site - The Old Breed I received an email this week asking if I can post this article up on here. A view from the site. Written by...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top