Recently changed plug sockets and light switches. Have noticed before this was done we were burning through light bulbs.

A few of our plug sockets are high voltage 250 -270.

Any ideas
 
If you have 270 V between live and neutral then yes, that is a little high. How did you measure this?
 
Recently changed plug sockets and light switches. Have noticed before this was done we were burning through light bulbs.

A few of our plug sockets are high voltage 250 -270.

Any ideas

250V is normal for the UK, this is what most substations are set up to supply.
270V is above the normal limits and if this has been measured with an accurate calibrated meter you should contact your distribution network operator ASAP to report the fault.
 
As far as I know no but I do know one of them might as they r changing alot within there house

You and your neighbour both need to contact your supplier. Let us know what they say.
 
Its k I know I'm not an electrician. Just trying to figure this out as we have been trying to solve it all day and beginning to wonder if it's a larger issue
 
Recently changed plug sockets and light switches. Have noticed before this was done we were burning through light bulbs.

A few of our plug sockets are high voltage 250 -270.

Any ideas
That's not HV, just higher than normal LV voltage, what were/are you measuring the Voltage with?
 
It may not be your next-door neighbour but the house a few doors down that is on the same supply phase as you that has the problem as well.
We were doing a school a few years ago where the emergency light fittings kept on burning out this was due to the voltage at the fittings being 250v+ we contacted the lighting manufacturer who said that the fitting gear was up to 250v so got in touch with Weston Power who altered the windings at the sub-station.
 
We used a calibrated multi metre for measuring

How recent was the last calibration?
Ideally you would check the test results with another calibrated meter to double check the results.

Anything over 253V is above the normal limits and could indicate a problem, there are certain faults which can cause the voltage to rise at some properties and fall at others which can be very dangerous, you should contact your DNO and report the fault.

One thing which has been known to cause this problem is the theft of the copper N-E from a substation.
 
If you are sure you are getting voltage as high as 270V then you must notify the DNO. They are duty bound to do something about it within six months. I advise notifying them by registered mail as I know of cases that have dragged on for years as the date they were notified could not be proven.
 
If you are getting 270V, being 40V over nominal and 17V over the maximum permitted voltage, this should be reported by phone to the DNO as a matter of urgency. They will generally treat such as an emergency and send an operative to site to verify within a couple of hours.

An extreme over-voltage will normally be rectified quickly, whereas the more common 'same time of day' over- and under-voltages recurrences can take a week or so, as the DNO will usually log 2 or 3 days' data at the head to take away and analyse, before tapping down/up at the transformer.

@R-fur where does the six months come from?
 
I wonder if the OP got this sorted. The thread is over 2 months old.

I measured voltage in a house with my multimeter... got 292v !!

Checked again with calibrated tester - 242v....
Had me worried for a minute.
 
Flake 99 vs Fluke 117
Is there much in it?
They're both yellow... :D

A typo and the number 18. That’s the difference.

No, my little multimeter is just a cheap thing from amazon but I’ve had it a good number of years. Digital readout, buzzer continuity tester...
I used it for electronics at college... along with a soldering iron and a little tool kit with screwdrivers and snips.
I keep it in the bottom of the toolbox just for quick continuity tests of fuses, cable identification etc.
 
TonyMitchell
I understand that the regulator puts the six month time limit on voltage complaints, if the DNO does not fix out of tolerance voltages in that time they can be penalised.
I havent checked this recently but a couple of years ago I got involved with a farmer, his wind turbine would not generate as the farm voltage was too high so he was loosing revenue. I got the customer to send a registered letter and the issue was resolved by adjusting the taps on the transformer. The time limit is more relevant for low voltage complaints as the DNO may have to invest time and money upgrading plant. I know of customers fed by a bit of wet string who have argued for years with the DNO.
 
This thread is a bit old, any new from @Alison about a resolution?

All UK electrical equipment should work, by design, from 216-253V as that is the official range of voltages (230V +10% -6%). Outside of that is probably a fault, certainly out of specification, and the electricity supplier needs to find and fix it.
 

Reply to High voltage plug sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
690
UK Strange
I am decorating our bedroom which only has 1 double socket in it. We have been using multiple gang sockets which are untidy and a trip risk, so I...
Replies
10
Views
477
Hi am just looking for some expert advice, my little girls room only has 1 double socket, currently have an extension lead with just the camera...
Replies
5
Views
193
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock