Just out of interest, what make/model of earth fault loop tester (presumably MFT) are you using? Some makes are better than others at no-trip Zs measurements through RCDs - on some you get "RCD uplift" of an ohm or so. I suspect the higher the Ze - particularly if it's variable - the more likely you'll get a discrepancy. Using the alternative method of measuring Zs, when there is an RCD present, is often the only way to get a reliable reading.

My concern about your high Ze is that it might be indicitive of a developing fault, one that's getting worse. It might be 1.14Ω this week, but if it's symptomatic of a breakdown in the lead sheath of the supply cable, it might well suddenly go much, much higher. You'll then be relying on main protective bonding for your RCD to work (assuming you've got metal pipes/anything else extraneous).

The DNO are within their rights not to supply a means of earthing if they don't want to. But I'm very surprised at their answer which seems to effectively be, "Yes, we're supplying an earth, but it's not a very good one, so bung an RCD on it."
 
Megger MDT 1553. A’s you say a calculation of the zs would be preferable now, as they have fitted front end RCD so can no longer by pass it for two lead test. Or possibly to fit an eart spike and convert to TT. But as you say I’m surprised that’s how they’ve left it, I’ve not been back to the job yet so I’m only going on what the home owner tells me.
 
In North West if we is between 0.8 and 1.6 then main fuse de rated and the faulty joint or whatever repaired. Between 1.6 and 20 a temporary RCD would be fitted and again the fault repaired. Over 20 if no RCD on consumer unit supply would be disconnected. The fault repair would be within 7 days, but usually done within one or two days
 

Reply to High ze readings. Even higher zs? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
477
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock